Arms
Reaction score
801
a fuse carrier is broken in 6way mem board with no rcd protection , it makes sense to upgrade to rcbos like other boards in the installation..

My question is , I'm nearly certain there is borrowed neutral on the lighting circuits and he won't want a wire fitted from kitchen to landing to separate and allow rcbos. Considering Its new board and requires eic, what's the rules on keeping the lighting circuits on mcb and eic
 
If it is domestic you have no choice other than to give additional rcd protection or note a departure and prove the absence of additional rcd protection leaves the installation no less safe than if an rcbo were fitted.
If it is commercial then installation methods may warrant additional rcd protection, if so you are looking at a departure as above.
 
From what I was told by the CPS , omitting RCD protection in a domestic job is pretty much a no go.
I can't see any situation in a domestic job where I would be happy to omit RCD protection.
 
I would go with @littlespark suggestion, make it a single lighting circuit so the "borrowed" neutral is no longer borrowed.

Not ideal as a fault will take out the lot, but in the days of LED lighting you don't need 2 * 6A total capacity, and far fewer trips due to filament lamps going 'pop' on switch-on.
 
Well I've got the job , so change fuse board then eicr for the the full installation. Which COULD acquire extra money .. that's how I left it..

Battery smoke alarms, reading building reg with smoke detection, it says battery units are ok if in date and RECOMMEND being hard wired when is to be changed .. source is building control NI , thoughts ??
 

Reply to Rcbo replacement fuse board in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
692
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock