Discuss RCD Issue, Tripping at half Limit... in the UK Electrical Forum area at ElectriciansForums.net
Hi All
I have just done a board change at a house that i'm sure is a TT System. (The House is supplied by overhead cable to the house with an earth rod net to where the external meter is fitted).
Once I had changed the board, I did a ZE Reading and GOt 5.63 Ohms. When testing the 30mA RCDs on the board it was tripping on half limit.
Has anyone experienced this with a TT System??
Had an RCD go down on a customer this morning. One ring final circuit with every thing on it kitchen, front room, hallway and backroom. I split the circuit in two and found the fault in the kitchen. Line to earth fault which took 3 hrs to find.
its ok, take you time .
we can wait for the answer.
Reply to RCD Issue, Tripping at half Limit... in the UK Electrical Forum area at ElectriciansForums.net
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
I try to keep out of Domestic work but I have a problem at home. Currently I have a wylex fuse board with re-wire fuses. they are great because...
4K