Discuss RCD tripping even with all MCB's off when it was a LINE to earth fault. in the The Welcome Forum area at ElectriciansForums.net
Lawmal
Hi, can anyone please explain this situation. 30mA rcd was tripping in a domestic installation. I narrowed it down to a lighting circuit but even with all McB's off, the rcd kept tripping, so I naturally imagined that it mus be a neutral to earth fault. In fact i discovered the problem and it was a clearly visible LINE to earth fault. Why was the RCD tripping even with all mcb's off when it was a line to earth fault?? The RCD was only tripping if the bulb was in the luminare, when I removed the bulb the Rcd only tripped when the Mcb was on and the fixture lighting turned on as naturally it does when it is a line to earth fault. But when the bulb was in the affected luminare the rcd kept tripping with all mcb's off!!
Reply to RCD tripping even with all MCB's off when it was a LINE to earth fault. in the The Welcome Forum area at ElectriciansForums.net
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
My circuit panel has two banks of breakers, each bank protected by an RCD. One of these RCDs has been problematic in that it trips intermitantly...
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...