Hello, ive just been at a job today which i will be returning tomorrow which i have a problem with 2 Ring mains on the RCD,

*1 RINGMAIN 1
*2 RINGMAIN 2

Now when i switch on the RCD, and NO mcb's are on, the Test button doesnt work, and its the same when the mcb's are switched,

Then i tried disconnecting 1 of the neutrals from RINGMAIN 1, and put the RCD back on, the test button now works?

Why would this be happening? and is it a N-E fault, if so why doesnt the RCD trip straight away when the power is put onto the Circuits?
 
Have you tested it properly with a tester, have you mixed up the supplied neutrals, does your meter show a neutral eth fault ?

Martin
 
N-E faults can sometimes cause weird effects with RCDs. get the IR tester on the job.
 
no lads, havent had a chance to megger it yet, but i'm just wondering as to why the RCD Wont trip with that Neutral connected, as soon as i take that 1 leg of the neutral out its trips no problem with the test button?? :/
 
wylex board, with a TNC-S, But im trying to get my head round this"As to why the RCD Wont trip with that Neutral connected, as soon as i take that 1 leg of the neutral out its trips no problem with the test button?? :/"
 
similar. a N-E fault on 1 RCD in a dual RCD board can cause the other RCD to trip. just a question of dissing all the neutrals, unplugging all appliances, then IR testing each one.
 
similar. a N-E fault on 1 RCD in a dual RCD board can cause the other RCD to trip. just a question of dissing all the neutrals, unplugging all appliances, then IR testing each one.

So basically ive gotta get into my head that RCD's can be a right pain the a**e then basically? and the N-E fault will also cause the RCD test button to not trip, if the test button is used? but why is that do you think? why didnt the RCD TRIP straight away when power was put onto the circuits????
 
Found this..... could this sum up my problem a little bit?????

1/ All MCB's off so even if power is on to the supply side of the RCD, there is no current flowing through the RCD yet cuz no loads switched on?

No current flowing so RCD wont trip even with a N-E fault present.


2/ If you had got some of your MCB's on with some appliances or lights switched on somewhere in the property I suspect the RCD would have tripped cuz current could now bypass the N half of the RCD through your N-E fault.


3/ Is the supply on the installation PME/TN-C-S..
i.e. Neutral and Earth joined together at the suppliers main cut-out?
cuz this will give you the symptoms you are describing:-

I will try & explain:-

Have a look at figure 11.1 on page 93 of the On-Site-Guide.

IF PME/TN-C-S, you can draw an connection between the N & E on the bottom left hand side of the drawing..

Now also put another connection between the N and E just before the load on the bottom right hand side of the drawing. (your N-E fault)

Remember the brown live wire from the RCD to the load would be open circuit because your MCB's are off..


Now lets consider a possible test current path...

  • From Live
  • Up the black wire to the test button
  • Through the test button
  • Through the test trip load resistor
(This is where it can now take two paths)
  • (i) Along the neutral through the RCD coil

    or
  • (ii) Along the neutral wire toward the load
  • (ii) Through your N-E fault
  • (ii) Along the Earth wire
  • (ii) Back from the Earth to the Neutral at the PME/TN-C-S connection.
If this is a PME/TN-C-S earth arrangement the two paths will probably be of a very similar resistance so the fault test current will most likely divide equally down the 'N' and the 'E'.

So the little bit of current flowing through the N coil of the RCD is probably too small to cause it to trip!


If Earth arrangement is TN-S or TT the resistance via your N-E fault down the earth conductor will be higher so the test fault current going down the E will be less..

So more will go down the N coil of the RCD and provide enough to trip the RCD with the test button!
 
So basically ive gotta get into my head that RCD's can be a right pain the a**e then basically? and the N-E fault will also cause the RCD test button to not trip, if the test button is used? but why is that do you think? why didnt the RCD TRIP straight away when power was put onto the circuits????
Kev the RCD test button is the last test you have to do after you test continuity of protective conductors,insulation resistance,polarity,Zs,RCD test +/_ Cycle and then pres the test button by using proper instruments and that will clear your mind.
 
Kev the RCD test button is the last test you have to do after you test continuity of protective conductors,insulation resistance,polarity,Zs,RCD test +/_ Cycle and then pres the test button by using proper instruments and that will clear your mind.

yea i know all that, i will be doing that tomorrow!, but im just trying to fathom out why the rcd wont trip with the test button at the moment,

does this sum it up....????
1/ All MCB's off so even if power is on to the supply side of the RCD, there is no current flowing through the RCD yet cuz no loads switched on?

No current flowing so RCD wont trip even with a N-E fault present.


2/ If you had got some of your MCB's on with some appliances or lights switched on somewhere in the property I suspect theRCD would have tripped cuz current could now bypass the N half of the RCD through your N-E fault.


3/ Is the supply on the installation PME/TN-C-S..
i.e. Neutral and Earth joined together at the suppliers main cut-out?
cuz this will give you the symptoms you are describing:-

I will try & explain:-

Have a look at figure 11.1 on page 93 of the On-Site-Guide.

IF PME/TN-C-S, you can draw an connection between the N & E on the bottom left hand side of the drawing..

Now also put another connection between the N and E just before the load on the bottom right hand side of the drawing. (your N-E fault)

Remember the brown live wire from the RCD to the load would be open circuit because your MCB's are off..


Now lets consider a possible test current path...

  • From Live
  • Up the black wire to the test button
  • Through the test button
  • Through the test trip load resistor
(This is where it can now take two paths)
  • (i) Along the neutral through the RCD coil

    or
  • (ii) Along the neutral wire toward the load
  • (ii) Through your N-E fault
  • (ii) Along the Earth wire
  • (ii) Back from the Earth to the Neutral at the PME/TN-C-S connection.
If this is a PME/TN-C-S earth arrangement the two paths will probably be of a very similar resistance so the fault test current will most likely divide equally down the 'N' and the 'E'.

So the little bit of current flowing through the N coil of the RCD is probably too small to cause it to trip!


If Earth arrangement is TN-S or TT the resistance via your N-E fault down the earth conductor will be higher so the test fault current going down the E will be less..

So more will go down the N coil of the RCD and provide enough to trip the RCD with the test button!
 
Does sound about right to me, Rcd's do funny things when a N-E fault is present and now you mention it wylex have done that to me on the last two i've tested. It won't trip on test button but will go randomly but when you test at x1 you will get a very fast trip time like less than 10ms. Any overly fast times normally that you would not expect to get usually ends up a N-E fault.
Am sure your IR test will confirm as tel says.
 
Does sound about right to me, Rcd's do funny things when a N-E fault is present and now you mention it wylex have done that to me on the last two i've tested. It won't trip on test button but will go randomly but when you test at x1 you will get a very fast trip time like less than 10ms. Any overly fast times normally that you would not expect to get usually ends up a N-E fault.
Am sure your IR test will confirm as tel says.

in that explanation what is meant by this

  • (i) Along the neutral through the RCD coil

    or
  • (ii) Along the neutral wire toward the load
what exactly is meant by this?
 
Think you have to remember an rcd has two coils and its the current produced between them that operates. In theory if you have a N-E fault the neutral will have no potential and if no current is drawn on the live both coils will be at unity.
 
Think you have to remember an rcd has two coils and its the current produced between them that operates. In theory if you have a N-E fault the neutral will have no potential and if no current is drawn on the live both coils will be at unity.

yea i think i know what you mean...

could you explain a little further, as to what was meant by the two points i put on just before your reply there?
 
It means in this state it becomes transient or floating even eliminating an actual load which is what is required to operate.
The term load referers to the current actually being produced which is an end product or resultant.
 
It means in this state it becomes transient or floating even eliminating an actual load which is what is required to operate.
The term load referers to the current actually being produced which is an end product or resultant.

and the reason this happens is, that the live comes into the rcd and trys to go through the coil, but why is this stopping the test button from working ?
 
and the reason this happens is, that the live comes into the rcd and trys to go through the coil, but why is this stopping the test button from working ?
The transient state cancels out some of the fault, I don't know any planner way of explaining.

If i had a heavy weight in my hand I would drop it as it was too heavy. If you helped me carry it, i may not drop it as it is not as heavy. sorry not the best analogy (can hear tel laughing) but best i can do with a glass in my hand.
 
The transient state cancels out some of the fault, I don't know any planner way of explaining.

If i had a heavy weight in my hand I would drop it as it was too heavy. If you helped me carry it, i may not drop it as it is not as heavy. sorry not the best analogy (can hear tel laughing) but best i can do with a glass in my hand.


so in this case for my RCD, there is some current flow returning on the neutral and earth, but not enough to trip the rcd using the test button is that correct? sorry haha
 
obviously im wrong en :(
No your correct, your trying to think too deep. Its easier than you think mate.
If its not tripping its because there is not enought fault current actually being seen by the rcd, hence why it becomes vague. you can press it 99 times and nothing happens, press it once and it may trip.
 
Last edited:
No your correct, your trying to think too deep. Its easier than you think mate.
If its not tripping its because there is not enought fault current actually being seen by the rcd, hence why it becomes vague. you can press it 99 times and nothing happens, press it once and it may trip.


Yea im sorry needaspark, its probz is easier than it looks, im always trying to think too hard when it comes to things like this, i just need to try and think it through easier ya know, just need to find an easier way of knowing it,

If you have time could explain a healthy circuit, and then a N-E Fault, as to why the button works ok on a healthy circuit and not when a N-E fault thanks.
 
An RCD cannot create an fault earth path when you press the test button as it has no earth conection so it creates its own inbalance by reducing the induction on the neutral coil so for instance if both coils had 100 turns and i induced a voltage with a resistor partway on one coil (neutral) at say 50 turns it would unbalance the coils and trip. if some of this current became transient and some went through the neutral coil and some went via and earth path it may not generate enough flow for the device to operate, in effect cancelling itself out. conversly if the neutral path to the coil was a shorter route (when you disconnected the neutral) it would leave no other route so would trip.
 
Last edited:
An RCD cannot create an fault earth path when you press the test button as it has no earth conection so it creates its own inbalance by reducing the induction on the neutral coil so for instance if both coils had 100 turns and i induced a voltage with a resistor partway on one coil (neutral) at say 50 turns it would unbalance the coils and trip.

With this mechanism the RCD test button would only work if there was a load current flowing at the time of testing.
 
An RCD cannot create an fault earth path when you press the test button as it has no earth conection so it creates its own inbalance by reducing the induction on the neutral coil so for instance if both coils had 100 turns and i induced a voltage with a resistor partway on one coil (neutral) at say 50 turns it would unbalance the coils and trip. if some of this current became transient and some went through the neutral coil and some went via and earth path it may not generate enough flow for the device to operate, in effect cancelling itself out. conversly if the neutral path to the coil was a shorter route (when you disconnected the neutral) it would leave no other route so would trip.


When you mention about me taking the neutral core out the neutral bar, and your saying that then means the current all returns too the RCD and return to the coil and it will operate the Button is that correct?
 
Correct, I think it used to be called a sensing coil that the flux is created by but its been a while since i've I was at college so I;m sure someone will correct me,

yea im beginning to understand now what you mean, so when the faulty neutral was taking ouf of the neutral, the current flowing in the neutral live are now the same hence why it is allowed to trip on the test button is that right Needasparks?
 

Reply to RCD tripping using test button, N-E earth fault. in the Australia area at ElectriciansForums.net

Similar Threads

Long shot but thought I’d try, have a lighting circuit that trips the RCD as soon as the neutral touches the neutral bar for said RCD. Bypass that...
Replies
6
Views
2K
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
379
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
383

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock