If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Doing refurb, total rewire & new DB, it’s a remote building, utilising Swa sub.
Swa is a 2c 16mm, there is main water & gas to be bonded, At moment this all connects to old DB, in my opinion this does not comply, given my recommendations, client refuses to pay extra for what’s been ok for years, shall I walk away.
 
depends on whether or not the SWA armour is equivalent to 10mm copper as a combined earthing and bonding conductor. i doubt it with 16mm SWA.
 
  • Like
Reactions: Pete999
Change the water and gas pipes to plastic
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Refurb what’s next
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
cliffed,
Last reply from
Andy5678,
Replies
2
Views
872

Advert