The are a few issues showing up here, and suggest BC are called in to confirm. The use of double lined 12mm plasterboard is required for ceilings, the use of heat detection in entrance areas is down again to local BC. Two problems are showing here, regs and practical risk assessment. You need to consider containment of fire, by building construction, reduced false alarm activation, the means of safe escape without panic and inproved safe passage...all covered in doc B....I really suggest before going any further, that your local BC are informed for their advice, they will have the final say no matter......please keep us informed, as this is a common area , where problems arise. and will help you as well as othersI'm lost now!
It is a mixed system, with part 6 (D) inside individual flats and part 1 (A) communal - operating side by side but not linked together. Correct
Each flat has a seperate grade D system- inside, not linked to any other flat or anything else. The grade D system has a smoke detector inside the flat. This won't disturb other flats if there is a false alarm but it will alert the occupant of the flat it is sited in. Correct
The communal hallway and 2x landings have a grade A system, with smoke detectors on the escape route, and a heat detector inside each flats entrance door (rooms opening onto the escape route). This seems to be common practice around where I live, and recommended for this type of building in a few different guides (3 story converted to flats prior to 1991 building regs, poor fire compartmentation etc). Controlled Document B 2007 and new EN54 2012...But Local BC will have final say.
What would be the point in a fire alarm that's only guaranteed to be heard on the stairs where the fire is? You wouldn't have to walk very far to realise there was a fire anyway. There wouldn't be any false alarms from burnt toast etc as the communal fire alarm detection in the flat is a heat detector inside the entrance door (rooms adjoining the escape route). Again Local BC to state
I've seen the last 2 fire risk assessments and notices, and the policy in the building isn't to stay put in the event of a fire but to leave immediately upon hearing the alarm. Risk assessments have shown fire alarms are not required in multi storey dwellings, and the sit and wait proceedure is standard practice in the UK
I think you've misunderstood what I mean.
Thanks anyway