Hi all

Keep getting pulled up by my gaffer to fix my earth continuity readings!!! Am fully aware that in a ideal world that my earth should be 1.67 x higher than live and neutral!!! however my last test sheet to be thrown back at me had 0.32 live and neutral and 0.62 earth continuity!! the earth was defo a 1.5!! yes it should be about 0.53 but i am testing some very old installations!!!is my gaffer right and the readings should always match the calculations as am close to taking him to the car park and beating the **** out o him!!!!its getting beyond a joke am even taking every socket of no to ensure no loose connections!!!:mad:
 
Tell you gaffer to get off his lazy arse and learn his job, their is nothing wrong with small variations in the readings, parallel paths, small variations in the terminal tightness etc all play a part as long as its not way out and your earth loop is under permitted value your fine.
 
If your testing new installs you should expect to get results as per the calculations, but in practice this doesn't always happen. Your doing periodics so you should be looking at the calculation as a ball park figure, i've been doing loads of periodics lately, and hardly every get perfectly matching figures! as long as its there abouts and you've checked the connections then you can only record the results you get. the readings you have sound fine.

sounds to me like your gaffa is a tw@! does he actually know how to test? You could suggest that you ignor the tester and just write down what he wants to see!

i have the same sort of problem, my gaffa rings me up telling i've done certs wrong, i just calmly tell him to read his regs, on site guide and guidance note 3, and tell him HE is wrong! usually takes a few days for him to work out hes full of sh#t and stops bothering me!

If you do go to the car park just make sure the CCTV is off!!!!
 
He is certinalty being 'picky' if it was me i would ask him to explian why he thinks it should be exaclty 1.67 etc, as already said there are so many reasons that can affect the end results. I would think that he would't be able to give you a good explaination?
Regards
AJ;)
 
interestingly, i had the very same problem on my niceic inspection and as some of the installation was over around 20 years the earth in the 2.5 t&e was only 1.0mm i did not notice this at first and the reading i was getting was double not the 1.67 ratio that is given in the osg
 

Reply to ring c.p.c readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Replies
9
Views
519
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top