i think I have lost the plot on this one
You have changed a consumer unit
You have verified a ring final has end to end continuity
You have established Zs on each outlet is within limits
You have spent days looking for and worrying about probable parallel earth paths that are making cpc readings better than expected
If this was a new installation and this were initial verification, then all well and good,but this is a consumer unit change,the circuit has been established as safe for reconnection,that is what you are expected to ascertain
You have the probable reasons why the readings vary and could answer the assessors questions if required
Why rip an "existing" installation to bits to find what can be explained by installation variations that are usual and often present