Would it be acceptable to have 4 ring mains, 1 for each floor of a 4 storey house? Washing machine and dryer are going in the basement and not the kitchen, or does the kitchen need its own feed? The CU is in the basement.
 
Last edited by a moderator:
I would personally put 4 radials in, the basement in 4mm from a 32A MCB the rest in 2.5mm on a 20A MCB, with the kitchen on its own supply
 
The kitchen will only have a fridge and toaster kettle etc, and there will only b 5 more dble sockets on that floor as well as the kitchen, would it not b ok to have that as a ring?
 
Last edited by a moderator:
There isn't a right and wrong way, everyone would do it different, but yes it would be acceptable (as long as volt drop and Zs are ok)
 
Its all about what you may expect to be on the circuit, if you are happy that the load on a kitchen radial will not exceed the 20 amps then thats fine
as said, obviously the basement with the heavy loads need a bit more, personally I would install a ring there because what you might gain in time not running that final leg you may well loose out in cost of the cable and it would be slightly easier to install 2-5
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
ring mains
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
IRB,
Last reply from
IRB,
Replies
6
Views
1,489

Advert