Discuss Ring off a ring ! Help please in the UK Electrical Forum area at ElectriciansForums.net
Hi, I know you can’t put a ring off a ring, you should join a cable in the back box of a socket, take it to your new socket, then continue the ring until you get back to your original socket
But I don’t know the reasoning why you can’t make a figure of 8 ring main if you like,
Could someone help me please
Many thanks
Hi Jordan and welcome.
As per @M-Ty, its a point load on the original ring with a bunch of outlets. So you’d need to connect it by a 13A fuse. If you preserved the original ring the 32A rating extends to the new bit, as long as the new ring meets earth loop impedance limits.
Mathematically I think it's no different to a lollipop circuit but testing would be a pain in the rear and I can't think of a single instance where extending the ring wasn't the easiest option.
I'll be honest I can't see the need or use for it.
Also why would you wanna do that.
If I’m adding 3/4 sockets of ring I usually come off to a unswitced spur then radial to power points,obviously in local area.some of these new houses are a mare to add anything new,ie: chipboard floors,Also your not the disturbing the ring as such,
A diagram to show the potential for overload as described by M-Ty using some possible current loads (obviously chosen to overload the cable)
You would have to work at it to overload but it is more likely and you would not need to overload the MCB to do it.
Many thanks
First of all have you tested the circuit you wish to extend are the readings acceptable
Although not dangerous in theory if there were a break in one of the legs after the cross over this would not show on an end to end test on a c.u. or d.b. therefore leaving one leg liable to overload. Or so my understanding leads me to believe.
Thanks guys! I just passed my AM2 and completed my NVQ, after telling my dad he’s extended the ring in the wrong way, he still knows best! I just didn’t know the reasoning behind it!
Thanks for your help and welcoming me onto this site
Get you dad signed up on here quick.
Reply to Ring off a ring ! Help please in the UK Electrical Forum area at ElectriciansForums.net
Hi all I would like to put some sockets in the attic and keep them on the main house ring main. Am I right in saying I can pull one of the legs...
Hi guys. Having a weird problem in a house that has suddenly happened. One half of the ring main has 240ish volts (fluctuates of course), and...
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
