B

bemmer2

100 amp box in house and have only 1 open slot for breaker ! I want to wire my new shed with 2-3 led lights and several outlets . Shed is 50’ from house box . Should I install a 30amp + breaker in the open spot and run #10 wire to a small sub panel in the shed or what might work better ? 220 not necessary at this time . Thanks
 
one for Megawatt . most of us are UK based and ain't got a scooby on US regs. and standards. ( with the exception that in the US, if it does not go bang, it's fine ?).
 
  • Like
Reactions: Megawatt and DPG
100 amp box in house and have only 1 open slot for breaker ! I want to wire my new shed with 2-3 led lights and several outlets . Shed is 50’ from house box . Should I install a 30amp + breaker in the open spot and run #10 wire to a small sub panel in the shed or what might work better ? 220 not necessary at this time . Thanks
Yes you can do that but make sure that the wire is rated for outdoor and direct burial if your not going to install conduit. Make sure the panel you buy is a main lug only and your shed has to be GFCI protected.
 
Yes you can do that but make sure that the wire is rated for outdoor and direct burial if your not going to install conduit. Make sure the panel you buy is a main lug only and your shed has to be GFCI protected.
Thanks ! My choice for box . Yes I will be using conduit to bury and ground fault protected !
 

Attachments

  • 054A7EFD-55C4-458A-9BB3-CF4DB3E111B8.png
    054A7EFD-55C4-458A-9BB3-CF4DB3E111B8.png
    492.5 KB · Views: 47
Yes you can do that but make sure that the wire is rated for outdoor and direct burial if your not going to install conduit. Make sure the panel you buy is a main lug only and your shed has to be GFCI protected.
Thanks ! I think I might have a problem , I ran 10/2 from a new 30amp breaker I installed my house service . I started wiring the shed today and Used the 30 amp box shown . I’m not sure but I think I should have ran 10/3 wire to allow the two breakers to be used ? Is there a way to use the 10/2 already ran and have power to both breakers ? I do not need 220 v at this time .
 

Attachments

  • C7F7B3BC-BCC2-4B92-9AE8-8C0268B44AF8.png
    C7F7B3BC-BCC2-4B92-9AE8-8C0268B44AF8.png
    491.8 KB · Views: 43
Thanks ! I think I might have a problem , I ran 10/2 from a new 30amp breaker I installed my house service . I started wiring the shed today and Used the 30 amp box shown . I’m not sure but I think I should have ran 10/3 wire to allow the two breakers to be used ? Is there a way to use the 10/2 already ran and have power to both breakers ? I do not need 220 v at this time .
Can I jump from 110 feed to other post ?
 

Attachments

  • 0C895B3D-BC81-4973-B556-B51B9003D51C.jpeg
    0C895B3D-BC81-4973-B556-B51B9003D51C.jpeg
    355.5 KB · Views: 43
Thanks ! I think I might have a problem , I ran 10/2 from a new 30amp breaker I installed my house service . I started wiring the shed today and Used the 30 amp box shown . I’m not sure but I think I should have ran 10/3 wire to allow the two breakers to be used ? Is there a way to use the 10/2 already ran and have power to both breakers ? I do not need 220 v at this time .
You have 2 lugs on top of the panel and right now you only have one wire in it so just install a jumper to the other side. Yes anytime you want to do a project like that, at least pull 3 conductors with a ground
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shed wiring ?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
bemmer2,
Last reply from
Megawatt,
Replies
6
Views
1,930

Advert