Thanks for coming back Julie. So i took the measured PSCC at the end of the circuit, 105A. K of 115, CSA 2.5mmYes
But using the actual disconnection time from your Zs, 95% voltage and when hot.
7.49seconds. Looking at the current graph, for a 20A C type MCB is around 18s. It will overheat. Correct? If i downgrade to B type, it,s less than .1. How would i apply the worst case scenario’s you describe?