Yes

But using the actual disconnection time from your Zs, 95% voltage and when hot.
Thanks for coming back Julie. So i took the measured PSCC at the end of the circuit, 105A. K of 115, CSA 2.5mm
7.49seconds. Looking at the current graph, for a 20A C type MCB is around 18s. It will overheat. Correct? If i downgrade to B type, it,s less than .1. How would i apply the worst case scenario’s you describe?
 
Thanks for coming back Julie. So i took the measured PSCC at the end of the circuit, 105A. K of 115, CSA 2.5mm
7.49seconds. Looking at the current graph, for a 20A C type MCB is around 18s. It will overheat. Correct? If i downgrade to B type, it,s less than .1. How would i apply the worst case scenario’s you describe?
The issue is to find the worse case, it may be when the Zs is 230V/105A - use the trip time for 105A - compare the time from the adiabatic to the trip time for 105A, but also when the same Zs is on 95% voltage, and hot (1.2x Zs) - which means actually a lower fault current, this would give a longer acceptable time from the adiabatic, but would also result in a longer time to trip.

You would have to calculate both cases as you can't really predict which will be worse. Higher currents are bad from the adiabatic point of view, but result in quicker trip times, so actually can help overall, but in other cases the lower current allows longer adiabatic time, which may actually be better even though it results in longer trip times.

The problem with 105A though, I think it will be the same trip time (or very similar) for both type b and type c

So actually unless you can drop the protection down (16A?), then you must increase the cable size, which not only reduces the Zs, but increases the capacity via the adiabatic.
 

Reply to Significance of 2.18ohns in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
945
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hello ! I am building for some time a cct to drive a 3digit multiplexed LCD. (from aliexpress) From the sellers on aliexpress I managed to find...
Replies
7
Views
1K
I'm fitting one of the Apex 7S units on Friday. I'd avoided the original range after a couple of bad experiences but I figured a new model might...
Replies
6
Views
823
You might remember this delight from the dodgy trade pictures thread.... I finally got back to quote for sorting today. The chicken and egg...
Replies
26
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock