Is there a certain cable size which enters into the house into the main cut out?

Or what are the most common?

Can you tell me the size of the cable in photo.

Thanks

E9EFE4F8-034A-4693-9D3D-AC818A3CC709.jpeg
 
A standard domestic house service supply will generally be 25mm² or 35mm² concentric cable the centre single core being the line conductor and the outer helical wound concentric conductor being the combined neutral and earth.
The cable in the picture looks fairly standard and fairly old, it is not possible to specify exactly what cable size is there but it is probably 25 or 35 mm².
 
As above, but most old service cables will be 16mm copper concentric. If it's over head fed it will be copper. If it's underground fed it could be Hybrid concentric. So a solid aluminium phase with copper neutrals. A 25mm hyb will have a 25mm aluminium phase with 16mm copper neutral. And a 35mm hyb will be a 35mm aluminium phase with 22mm copper neutrals. 35mm copper concentric is rare but occasionally used. Most mains Lv underground cables from the sub are now aluminium phases with copper neutrals called wave con or wave form cable. Most new lv over head is stranded aluminium insulated known as ABC
 
Sometimes and looking very similar a 'split concentric' cable is used whereby the outer helically wound conductors (N(ins'd) & E) are separate.
Still seen this recorded as TN-C-S (PME) though.
 
Sometimes and looking very similar a 'split concentric' cable is used whereby the outer helically wound conductors (N(ins'd) & E) are separate.
Still seen this recorded as TN-C-S (PME) though.

That's interesting. Are the N&E conductors joined at the cutout though? It would just be TN-S otherwise surely?
 
Yes split concentric is TNS, the outer concentric neutrals strands will be individually insulated and the earth strands will be un insulated. However back at the mains joint it will often be connected to a 3 core CNE (combined neutral earth cable) so neutral and earths connected togerher in the joint. Unless connected to an older 4 core paper lead cable in which case they will be kept separate.
 

Reply to Size of this cable. Main cutout in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
528
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
867
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
269
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
617
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock