Damian Petsas

Ive just completed my first Domestic Pir and come across some odd values for r1+r2 and for insulation resistance on a fair few of the circuits. I would really appreciate some guidance with this to put my mind at ease.

Ring final circuit values ranging between 0.73 -0.92 ohms and getting 0.32 M ohms for my insulation resistance for phase to neutral ???? or even what would seen dead 0.01M ohms. My main concern is that on most circuits when testing insulation resistance i was getting a odd reading for one test and then a passable one for the other??

Ally guidance and wise knowledge would be greatly appreciated.

Many thanks guys .
 
Your IR suggests either a breakdown in the insulation or something still plugged in. The continuity readings don't mean anything really mate, how long is the circuit?
 
Sound like you could have a few issues,
1- did you remove all items from sockets and lamps etc
2 - It is actually an EICR not PIR
3- what are your issues with R1 R2
 
I think i got everything disconnected could the neon on a faceplate cause it?? or lamps connected in a lighting circuit even if tested at 250v
 
so if i remove all lamps that should solve my issue over the ir on lighting circuit then?? i take it i gottal link out dimmers too( ball ache)

- - - Updated - - -

I know i mush come across useless but thought 250 v was to allow for testing such accessories without disconnection
 
On an eicr you can test L+N together against CPC. You normally do a soft test @ 250 to check for remaining loads before the 500 test. They don't like it up em you know.
 
i have mainly been doing commercial install works and v v little testing but gotta start somewhere i suppose. thanks for the headsup Geofsd so the values varying between 0.73-0.91 are ok?
 
so the values varying between 0.73-0.91 are ok?
It's not tooooooo bad.

If you mean these are the results at different sockets being tested with a plug-in tester lead then I would suspect the socket contacts or the switches.

r1 of 0.73 and r2 of 1.21 is perfect for 2.5/1.5.
 

Reply to Some technical help please. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
886
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
712
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
309
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock