same thing IMO. never heard it described as Sp&N. though. just a D/P isolator, 1 pole for L and 1 pole for N.
 
one's fused and one isn't, according to what you have posted. sounds like the SP&N is the fused one. only the L can be fused.
 
A switch disconnector has to:-

Provide an effective clearance between the supply and the load appropriate to the voltage applied.
Provide a means of locking in the 'Off' position. (Padlocking)
Provide a true indication of the contact state.
Provide a safe disconnection from the supply even under fault conditions

A double pole switch dosn't have to meet all these set requirements.....

The two terminologies function the same more or less although when talking switch disconnectors you may also have 'early make - late break' on the neutral especially on 3ph... the uses of the 2 terms relates to requirements of the isolation needed...
 
So for single phase supply, any one of these can be used to isolate the main supply if needed to work. Difference is one with fuse and other without.
 
all depends if you need a lockable isolator.
 
A switch disconnector has to:-

Provide an effective clearance between the supply and the load appropriate to the voltage applied.
Provide a means of locking in the 'Off' position. (Padlocking)
Provide a true indication of the contact state.
Provide a safe disconnection from the supply even under fault conditions

A double pole switch dosn't have to meet all these set requirements.....

The two terminologies function the same more or less although when talking switch disconnectors you may also have 'early make - late break' on the neutral especially on 3ph... the uses of the 2 terms relates to requirements of the isolation needed...

Commonly called off load and load breaking, switch disconnectors!!
 

Reply to SP&N isolator and double pole isolator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
845
I have taken delivery of an undersink water heater. It is fitted with an RCD on the electrical supply cable which terminates with a euro-plug. I...
Replies
19
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi everyone, I have moved into a property with a 63a single pole rotary isolator controling a inline water heater. Is this safe? Surely it should...
Replies
17
Views
2K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock