Discuss SPD in RCBO board?????? in the UK Electrical Forum area at ElectriciansForums.net

SPD should (generally speaking) be fitted to all boards, though in some cases it might not be economically worth while (where surge risk very low and value of down-stream equipment also low).

When fitted SPD should be after the incoming switch and before and RCD or RCBO. Some SPD specify that a certain MCB should be fitted in the supply, but many of them are safe with fuse up to 100A or more and so do not require any specific protection, consult the data sheet to see (or buy a CU with the approved combinations pre-fitted).

In some cases you might have an up-front RCD as the main switch, typically for TT installations. That is an exception to the above rule of being before SPD, but it is normally a type-S (delay) RCD and typically they are rated to a higher surge current that the ones normally used for the "instant" protection of final circuits. They key point here is if the SPD is diverting a lightning surge then it might be passing of the order of 10kA, though usually only for a few tens of microseconds.

If you want an in-depth guide to lightning protection then this manufacturer's brochure is very good, but it is about 10MB PDF download and the SPD section starts on page 68:
Also worth having a copy of is the BEMA guide report here:

There are obviously other guides and suppliers, but not many have such a wide range of information in the one place.

TL;DR Fit the SPD immediately after the main switch, and keep the wires short and close together to minimise inductance.
 

Reply to SPD in RCBO board?????? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
236
Hi guys, could someone help with the following please? The scenario is: Domestic property supplied via three phase (with a 3P main DB, NO SPD)...
Replies
2
Views
501
Client needs an SPD fitting but no room in c/u or adjacent. Best bet looks like a parallel connection into the tail blocks in the meter cabinet...
Replies
3
Views
277
Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
823
I have a fuseboard change I need to do soon I’m putting in a FUSEBOX 7 or 10 way RCBO+ SPD My only concern is how I should run the pyro cables in...
Replies
16
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock