Discuss Spur from boiler circuit in the DIY Electrical Advice area at ElectriciansForums.net
Hi. I am wanting to install a regular single 13A socket (with RCD protection) near my boiler to power a Raspberry Pi, which draws comfortably less than 1A.
The boiler is on its own dedicated circuit protected by a 5A MCB at the CU and a 3A fused double-pole isolation switch next to the boiler itself. Boiler manual states power consumption of 152W so also less than 1A.
Is there any reason why I cannot add this new socket? And should I spur from the supply or load side of the isolation switch? Obviously the MCB (and/or switch fuse) would trip if anything more power-hungry was plugged into the new socket, but it will be inside a cupboard in the corner of a room, so wouldn't be much use for anything else anyway!
Thanks in advance! :D
That is not a suitable way of powering a socket.
You could put another fcu on the same circuit and that would be ok.
Reactions: DPG
Hi - the cable from the Consumer Unit may be the small 1mm type that’s used for lighting and it’s been repurposed to the boiler with a 3A fuse. We should not put a normal 13A outlet on that type of cable, sorry. An Electrician could tell you which cable has been installed and hopefully give you a cheap upgrade path.
Thanks for the responses, I understand. I will call someone in as it's not quite as straightforward as I was hoping. Hopefully there will be a quick and simple (and cheap!) solution. Thanks again (y)
Reply to Spur from boiler circuit in the DIY Electrical Advice area at ElectriciansForums.net
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
We have an outdoor socket that is hard wired into the ground floor power circuit and protected with an rcd in the consumer unit. I now plan to add...
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...