Discuss Spur from Ring Main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

A

andyh

I'm looking to spur off the ring main to supply an FCU for a fixed piece of equipment. The spur will be from an existing double socket. Question is whether it is ok to use 2.5mm cable or whether the connection to the FCU should be in 4mm? The FCU is fused at 13A so it can't draw more than this but what happens if there's a fault in the ring main supplying it causing a current in excess of what the single 2.5mm can take?
 
only reason i use 4.0 is before i have seen people spurring of a spur in 2.5, in which you end up with 3 or 4 sockets fed via a single 2.5 covered by a 32a mcb
 
Thanks for the replies. I always thought it was 2.5mm as standard. All I'm thinking about is the case where a current fault in the ring overloads the single 2.5mm or can this not happen? The 13A FCU protects the load side but what protects the link between the ring and the FCU?
 
only reason i use 4.0 is before i have seen people spurring of a spur in 2.5, in which you end up with 3 or 4 sockets fed via a single 2.5 covered by a 32a mcb

The regs don't allow spurring more than one socket though without fusing down, and I'm not sure spurring several sockets in 4mm off a 2.5mm ring would comply either? By the book I would have thought one socket per spur without fusing down, whether the cable is minumum required 1.5mm or oversized to 2.5, 4mm, 6mm or whatever. If someone comes along afterwards adding spurs onto spurs onto spurs that's something a competant electrician wouldn't do and we can't go overkill on everything just in case a DIYer decides to bodge more on there in the future.
 
as far i was aware you can spur of a ring in 4mm to several sockets as the cable is sufficient to carry the current? please let me know if this is incorrect.
 
The way I was taught was that:

Only 1 spur off any socket or juction point of the ring circuit.

No more than 1 double socket on that spur - unless the spur is protected by a 13A FCU.

Minimum cable size of 1.5mm for 13A FCU, 2.5mm for double socket.

The reason you are not allowed to spur off of a spur is to limit current draw through the terminals on the back of sockets to prevent overloading and overheating of the terminals of the original ring circuit socket.
 
Last edited:
as far i was aware you can spur of a ring in 4mm to several sockets as the cable is sufficient to carry the current? please let me know if this is incorrect.

Yes, that is incorrect, you will be overloading the ring at the point of connection.

Have a look in the back of the regs book at final circuit arrangements.
 

Reply to Spur from Ring Main in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
783
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
258
Hi all, My mother wants a double socket adding next to a desk, behind the desk there is a 10mm (i dont know the MCB in the Consumer Unit) which...
Replies
4
Views
1K
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
799

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock