Romans99

Right guys, apologies in advance for lack of detail etc but I've only had a very brief look at this one today and I'm expected to work miracles tomoro.

A three phase 13kw motor for an AHU extract fan was running very noisy and they sent it away to be refurbd
It has come back and been put back in.

It now runs for approx 20-30 seconds before blowing a 40amp fuse in the control panel.

Control is wired star delta and has not been altered, adjusted or messed around with.

Client is convinced it's wired wrong and want a quick fix.

I'm no expert on starters or indeed three phase motors,

Has anyone with more experience got any fault finding suggestions.

Why does it run for a while before blowing the fuse?

Again apologies for lack of detail but I'm back there tomoro and should now more then.
 
Is the starter switching to delta when the fuse blows

I assume by refurbed it has been rewound

If it is I would check that the motor connections are correct to the starter as motors do not normally come back rewound with the windings terminated onto the motor terminal block in the same order as they where taken out
 
Last edited:
Right guys, apologies in advance for lack of detail etc but I've only had a very brief look at this one today and I'm expected to work miracles tomoro.

A three phase 13kw motor for an AHU extract fan was running very noisy and they sent it away to be refurbd
It has come back and been put back in.

It now runs for approx 20-30 seconds before blowing a 40amp fuse in the control panel.

Control is wired star delta and has not been altered, adjusted or messed around with.

Client is convinced it's wired wrong and want a quick fix.

I'm no expert on starters or indeed three phase motors,

Has anyone with more experience got any fault finding suggestions.

Why does it run for a while before blowing the fuse?

Again apologies for lack of detail but I'm back there tomoro and should now more then.

Check the connections at the motor to make sure there are no links in place (links might have been installed for testing after refurb)
 
although the timing sounds wrong, you need to watch the contactors change from star to delta if this is when the fuses blow then its a wiring issue, what fuses are blowing surely the overload should trip first unless their was a motor fault, that is if its connected up right.
 
I would expect more than one fuse to blow if links were fitted in the motor


Agreed wasn't thinking properly.

Might be a cable not glanded back in to motor properly giving a fault to earth on the delta cycle.
 
Last edited:
I would firstly check that the connetiona are right at the motor... U1-V2, V1-W2, W1-U2..
If yo get your ones and twos crossed over, it creates mahem!

Also, drop all the connection outta the Starter (safely), AND start the Starter. If it run through the timed cycle then all the control circuits are ok, then back to the above;)
 
It could be that in STAR the motor is turning on way and when it changes to DELTA the motor is trying to go the opposite way. The motor needs to be belled out
 
Thanks guys
I ended up on a different job and didn't get back to this one,

Slightly relieved I didn't have to figure it out but slightly disappointed I didn't get the chance to figure it out!
 
Thanks guys
I ended up on a different job and didn't get back to this one,

Slightly relieved I didn't have to figure it out but slightly disappointed I didn't get the chance to figure it out!


Its a simple case of the new winding not matching up to the original, in future ask the rewind company to check the phase progression of the windings while there detailing it and put it back as it was.


I work for a rewind company and we dont check phase progression on small machines.
 
sounds like motors connected wrong,i would think 20s to 30s is too long for change over and could take the fuses out as youve no o/l protection in star

yours benji
 
Almost certainly that the motro is reversing when it changes from star to delta. When motors are rewound, very often the direction of the windings aren't considered.

You need to drraw the circuits out in star and delta and work out which winding you need to reverse to give a change in delta but not in star.
 

Reply to Star delta motor help in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
Hi I got called out to a faulty star delta starter on an old Stenner band saw Monday (was getting stuck in star and blow fuses) - So I ordered a...
Replies
19
Views
5K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock