Hi, I am a newly qualified spark and I just want to confirm I am doing this small job correctly.

The job is to swap my grandmas cooker and hob. At the minute she has a gas hob and electric cooker. There is a 10mm cable supplying a 45A switch with socket outlet backed by a 40A breaker. At the moment the cooker is wired in 2.5mm flex from the 45A switch direct to the cooker with the hob being plugged in on a 13A plug. I believe this is wrong as the 2.5mm cable from the 45A switch to the cooker is fused at 40A with the maximum load of the cable 20A?

The new cooker I am installing is 2.9kw and the hob is 6.5kw with the cable run being a maximum of 10m. That gives me a total load of 40.87A so the 40A breaker and 10mm is ok.

What I have in my head is to hard wire the hob into the 45A switch with 10mm and wire the cooker in 1.5 flex on a 13A plug top. The load for the cooker is 12.6A, is this to close to 13A?

Ideally I would run a seperate 20A supply for the cooker but want to avoid chasing down the wall if possible.

Also, would it be possible to wire from 45A to cooker in 6.0mm. I dont think it will because its fused at 40A and 6.0mm wont be big enough. Please correct me if I'm wrong.

Thanks in advance for any help.
 
Run a 6.0mm from the 45a switch to a low level cooker connection unit and connect the hob in 6,0mm....you'll struggle to get a 10mm into the hob connections. Loop a 2.5mm from the incomer side of the LL connection unit into a 13a socket for the oven.Mount these on two surface boxes butted up to each other. Replace the existing 40a breaker for a 32a....remember diversity on cooking appliances means they will never draw maximum current for any length of time if ever.
 
Last edited by a moderator:
10mm from load side of 45A switch to a dual box with a cooker outlet plate and on the other side a 1g socket. 4mm to the hob from the cooker outlet plate and plug the cooker in. No need to change the mcb.
 
Last edited:
Dual cooker outlet plate connected to the cookerswitch via 10mm T&E
6mm from one outlet to hob
2.5 from the other outlet to the oven

All done and compliant without hiding 13A fuses where nobody can get to them or adding extra cables to a finished kitchen.
 
I'd do the final connection to the hob in 4mm 3 core HO7 type flex too as it'll probably get way too hot under there for T&E over time.
 
Dual cooker outlet plate connected to the cookerswitch via 10mm T&E
6mm from one outlet to hob
2.5 from the other outlet to the oven

All done and compliant without hiding 13A fuses where nobody can get to them or adding extra cables to a finished kitchen.

Best check the oven requirements first,often these are designed to be fused at 13a via a plug.

To the OP all of the above are acceptable,personally I would still run 6.0mm from the 45a switch and drop to a 32a MCB if only because 10mm is a pig to terminate in a single box size accessory.
 
Last edited by a moderator:
Best check the oven requirements first,often these are designed to be fused at 13a via a plug.

Hahaha, you're kidding right? Appliances are not protected by plug fuses, cables are!

An oven is a fixed load not requiring over current protection, so cable size can be based entirely on the load current and not the nominal current. Plus the cable behind a built in oven is pretty well protected from mechanical damage, so what really is the problem?
 
Hahaha, you're kidding right? Appliances are not protected by plug fuses, cables are!

An oven is a fixed load not requiring over current protection, so cable size can be based entirely on the load current and not the nominal current. Plus the cable behind a built in oven is pretty well protected from mechanical damage, so what really is the problem?

I realize that,but some single ovens come with a fitted 13a plug....so I would suggest any other method of connection would be against manufacturers requirements. I didn't say there was a problem did I?,just to check manufacturers requirements....is it time of the month or something?
 
Last edited by a moderator:
I realize that,but some single ovens come with a fitted 13a plug....so I would suggest any other method of connection would be against manufacturers requirements. I didn't say there was a problem did I?,just to check manufacturers requirements....is it time of the month or something?

You said that ovens are often designed to be fused at 13A by a plug, high is a nonsense as the oven will not be fused (protected) by the 13A plug fuse, only the cable. Ovens are protected by their own internal protection (the overheat stat usually)

Time of the month, No, just ****ed off with the ridiculous bowing down to nonsense printed in manufacturers instructions and the mistaken belief that appliances fitted with plugs must never a have their plugs cut off.
 

Reply to Swap Gas Hob for Ceramic Hob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have bought a cooker with a ceramic hob which has a warning light to show that the top is hot, the light goes out when the hob cools down. I...
Replies
2
Views
733
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
398
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
235

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock