Have got a Three phase transformer wired in star on the 7th floor of a part built tower block and the builder wants another tranny on the 8th floor to supply the works on that floor.

There is already a single phase tranny on the 8th.. (not yet wired up)

Is it possible to take a single phase supply for the 8th floor single phase tranny from the three phase tranny on the 7th, using one of the phases and the star point as a neutral, or would this trip the RCD?

I really don't want to carry a 3 phase tranny up 16 flights of stairs.........:(
 
Would be nice if you expressed voltages here input and output....

What protection is there, what load are we talking is this a building site ???????
 
Would be nice if you expressed voltages here input and output....

What protection is there, what load are we talking is this a building site ???????


1) Input voltage is standard 415v (400v) nominal , output voltage is 110v

2) Circuit protected by 3phase 32A MCB, whole site protected by 100mA RCD on the generator

3) Trannies are 10KvA, and will be used to supply temporary lighting, and outlets for 110v volt equipment

and yes, this is a building site :)
 
Still Ambiguous - .... if you were to piggy back second transformer of the supply to the first as i see in your OP then the inrush on start-up would be a big issue if you thinking of taking it off the out-going side ??? then i assume youll have 110v between phases 55v to star point.... you kinda of lost me here unless you have a multi-tapped unit.

The primary current of a 10Kva 3ph transformer is approx 14amp per phase (requiring 25amp-D)
The primary current of a 10Kva 1ph transformer is approx 42amps (requiring 63amp-D mcb)

Either way you would have problems turning the units on as inrush would be cause for concern as well as the demand on the primary side of the 1ph unit.

A separate supply and est using the 3ph transformer is your best option IMHO unless ive mistook your info or you have missed anything out that is relevant.
 
  • Like
Reactions: 1 person
Hmmm some good points about start up current there Darkwood, .......but would it trip the RCD?
 
Rcd's monitor Earth Leakage which shouldn't be a concern for inductive inrush currents as the PH/N are still balanced throughout the inrush, although its not unheard off with some makes of rcd that the magnetic spikes within the rcd on inrush can create nuisance tripping. Most quality brands out there are not really prone to this as the inrush itself is usually over with within a few miliseconds.
 
I'd piggy back off of one of the incoming phases to the 7th floor tranny in singles (something like coil end cable) to an enclosure with a 2pole breaker in, bolted to the side of the transformer, then run an appropriately sized 3 core SWA up to your new single phase tranny on the 8th. Done.
 
Hmmm some good points about start up current there Darkwood, .......but would it trip the RCD?

I don't think you have caught on to what Darkwood is saying here. How are you going to piggy back off a 415V/110V 3 Phase TX with a single Phase TX 230V/110V??
 
  • Like
Reactions: 1 person
I'd piggy back off of one of the incoming phases to the 7th floor tranny in singles (something like coil end cable) to an enclosure with a 2pole breaker in, bolted to the side of the transformer, then run an appropriately sized 3 core SWA up to your new single phase tranny on the 8th. Done.

Did you not read my post on primary side current demands, if you piggy back of the supply side of the 3ph transformer then the supply to that transformer would need to handle 56amp + cable calcs as oppose to 14amps FLC also with a 32amp protective device there would be tripping issues, also will the 3ph supply to the 3ph transformer have a N?
 
For gods sake, get someone that knows what they are doing or at least what they are talking about!
 
Isn't he just on about a temporary site transformer here for **** sake?
Wouldnt it just be easier to take a new single phase supply from the same board thats feeding the 7th floor tranny, up one floor to feed the new one?
 
Last edited by a moderator:
No mention of a DB here at all its a building site with a 3ph Tx rigged up on 7TH floor, if OP had a DB to connect to I assume this thread wouldnt have been created and temp or not the install still has to comply
 
Isn't he just on about a temporary site transformer here for **** sake?
Wouldnt it just be easier to take a new single phase supply from the same board thats feeding the 7th floor tranny, up one floor to feed the new one?
Just thinking the same :) . . use 230 v single-phase taken from 7th floor (one line plus neutral) to feed the 8th floor 230/110 v single-phase transformer.
 
  • Like
Reactions: 1 person
The 3Ph transformer would be ∆Y therefore no neural on the primary input. He referred to using the star point, the only star point is on the secondary side. This star point should be earthed.

To get 230V from the ∆Y transformer the primary neutral would effectively be connected to earth and using the earth as its neutral conductor.

I hope I’m wrong but this has to be one of the most stupid and dangerous ideas suggested on here yet.
 
  • Like
Reactions: 1 person
Just thinking the same :) . . use 230 v single-phase taken from 7th floor (one line plus neutral) to feed the 8th floor 230/110 v single-phase transformer.

:) it seems to me (possibly due to limited info from the OP) that some are over complicating this.
The way I read the OP was that there is some sort of office refurb going on and there is an existing site transformer being used by trades and basically all he wants is an additional one on the floor above.
It does seem odd that it has an RCD protecting it but I have been on sites where trannys have been daisy chained, failing that just run another supply up one floor like we've said!
 
I read it as tony does too, its a building site... as we have been informed , if their was available DB's then the OP wouldn't be asking the initial question
The OP has explained the secondary is 110v on both TX's and in the case of the 3ph TX on Floor 7 it its primary will be 400v (No Neutral!) please explain where your going to get this N from Cossie.... i originally put this to the OP who clearly states i make good points ... if i was wrong in my thinking of the OP set-up he would have corrected me back then.

Far from over complicating things here we are trying to help the OP avoid a potentially dangerous set-up . ....but happy to see your oblivious to this if not a little scary, yes agree the info is limited but i wouldn't just say yes sounds ok without high-lighting the dangers and possible issues. This way the OP has all the info he needs to which he can make a decision .

If their was an option at to plug into a 230v secondary output on the 3ph TX (Noting the OP hasn't said this is the case) i would still way up the whether the TX was up to it long before i plugged it in this way you dont have to fob you way out of situations when the foreman complains the power keeps tripping. If i was to set up a temp' system on any site i was on it wouldn't bode well if the mcb's kept nuisance tripping or other related power problems nor would it give good impression.

I make my original assumptions to the fact that the OP states the TX's are 10Kva rated so i would suggest this is a large building site if they have a 3ph one fo the 7th floor hence caution to loading and were it doubtfully be at all possible to daisy chain as you suggest and given the 1ph TX is also 10Kw are you aware of the primary inrush current could be in excess of 600amps a mean feat of any mcb rated under 63(d) not to trip on power up..... so makes me wonder how the 32amp protecting the 3ph Tx will react?
 
Last edited by a moderator:
OK everyone calm down.

It is a bog standard tranny on a bog standard site. There is obviously a DB feeding it but it is on the ground floor and would involve a 50m run of armoured to feed one tranny, which would obviously cost money.

There are dozens of 3 phase trannies on this site and all are fed off type C 32amp mcb's, and have been working happily for many months with no nuisance tripping

I was obviously thinking about daisy chaining the trannies on the primary side, but have decided against it , and found a single phase tranny on the 7th to come off. This was done today and everything is fine.

I too have worked on sites where there are no RCD's but this one does have one, as I believe temporary installations are required to, when TT'd.

Anyway thanks for contributing in a positive way guys, as I am always keen to listen to people with constructive criticism .
 
At least your sorted and did say 25amp (d) for 10Kva so a 32(c) is understandable in that it doesn't or rarely trips.... when we have limited info we have to assume alot hence the threads can get deeper lol.... its the norm on here ;)
 
Yep as long as the new SP is protected properly
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Taking a single phase suply from a 3phase transformer.....
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
Crosswire,
Last reply from
Pete999,
Replies
19
Views
2,946

Advert