Hi we did a report today and the tails to the mk metal metal consumer unit were through two separate 20mm knockouts. We are now arguing if this should be C2 or C3. Also the main earth entered through the back of the unit. Any thoughts on this ?.
The regulations specify that L N and E may only be collectively enclosed by ferromagnetic material when entering an enclosure. And this has been a regulation for longer than MK have been making CU's so nobody can even say it complied with previous regs.
But is it potentially dangerous?
It isn't in normal use as the eddy currents from currents less than 100A are negligable. But under fault conditions there may be significantly more current flowing and much bigger eddy currents.
C3 , IMO. i phoned Eddy asnd he wasn't upseyt by excessive currents. in fact, he asked for more in his cookies.
Hi davesparks,
Thanks for your reply which backed up my thoughts.Although I did opt for improvement recommended to bring the installation to comply with the regulations. The consumer unit has been this way for about 15 years so I could not see how the lead electrician thought this was potentially dangerous
Reply to testing code for ferrous consumer unit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...