Search for tools and product advice,
Discuss TL inverters and TT earthing systems? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
R
Ross Harvey
HI
Im after a bit of advise.
Im a suby for british gas wiring heating systems. When a salesman goes to quote a job they have to do a "socket and see" test on a circuit to see if the main earth is sufficient. (not a great way to test it by hay-ho). Anyway this installation fails the test. so they send me in to do a proper inspection. It turns out that it needs the main earth upgrading. In this case we sell them an earth rod pack. This is where it gets interesting. The main cut out fuse for this installation is in a neighbours house (great!).Also he has a Sunnyboy 4000TL already installed. As this is a TL inverter i cant put the whole installation on a 30mA RCD.
So my question is can i put a 100mA RCD in instead?
I know some might say just get them to upgrade there earth through the DNO, but i would rather the work myself (selfish i know, but work is work).
Any advise would be appreciated.
I'd get the DNO out to sort the Earth out as Marvo said. And I would split the supply so that you got the house on its consumer unit and then install a 2 way consumer unit for the PV. That way you would have a 30ma on each consumer unit. It's recommended to install PV on it's own RCD to avoid nuisance tripping with all the combined Earth leakage of the house and PV
The pv circuit is already on its own consumer unit. But not on an rcd. TL inverters are not supposed to be protected by a 30 mA rcd. I new that getting the DNO to re new the earth would be best solution. I was just wondering if I could use a 100mA rcd instead of a 30mA.
Is there any reason why the TL inverter needs to be on an RCD? Such as how the array is installed or the route of the AC cable? If not, then what's the issue?
ETA Ah, now that I've read the thread properly, I see what you mean.
Surely getting the DNO out is the right thing to do. If a TNS is achievable then surely it is desirable over a TT setup?
Yes 100 ma RCD will be fine. You may actually find the Inverter manufacturers instructions state that it should be protected by 100ma RCD protection.
Don't see how you can say that, one of the issues is DC leakage and thus holding the RCD closed. Sibert will post you the appropriate technical documents from Doepke in Germany if you like.
100mA Type B I'd agree with, have you seen the prices of one of those though :) - Andy at Sibert will sell you one quite happily :)
I was aware that as the sunny boys AC/dc inputs are electrically separated there wasn't as issue with reverse dc currents??
High ze is DNOs problem. Call them out to sort the issue IMO :D
Reply to TL inverters and TT earthing systems? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Hello - hope someone can advise please. I have a recently purchased second hand Myford lathe which has a 3-phase inverter (Siemens Micromaster...