Just venting a little....
At 2:45pm I'd finished another job early. So I thought I'd have an initial look around a really small 2 bed bungalow due an EICR. It only has Lounge, Kitchen, small passage, 2 bedrooms and a bathroom. In my head this would be nice simple, almost relaxing end to the day.
The landlord was a pleasant chap and was totally honest that it hadn't been inspected since he owned it (15 years) or even when he bought it.

Unfortunately it didn't get off to a brilliant start. First 4 things I looked at:
1 - Mysteriously find TNS earthing abandoned (testing at 0.32 ohms) in favour of TT (89 ohms). I'd better mention that the property is currently vacant. I'll be trying to get DNO out in the morning to confirm the TNS is ok to use again.

1615913150591.png

2 - Gas bonding for giants on stilts. Closer to 600 cm than 600mm .
Then it got even better, when I tested it I got over 2 ohms, and further investigation revealed a large coil of abandoned 10mm cable in loft not connected to anything at all. The Landlord agreed best use of time today was to sort that before carrying on so I spent the majority of remainder of afternoon sorting that and moving it lower.


1615913289771.png
1615913337793.png

(On the plus side the mains water bonding was connected and worked.)

3 - Next, bathroom bonding conductor not connected. Ok, simple enough to fix.

1615913399069.png


4 - I turn to lighting - maybe a taster of what is yet to come....?!

1615913450433.png

The found all ceiling roses have 20 layers of paint on them and crack if you look at them and the kitchen fluorescent rotated on it's one screw when I put a probe on it.
Tomorrow I need to investigate why all of the kitchen sockets have really high resistance on the fixing screws compared to the R2 - I suspect metric thread extenders are loose in the original imperial lugs.

But to end on a positive note, at least the electrics in this place are finally being looked at.
Vent over. Thank you.
 

Reply to Todays bag of fun in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
414
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I am renovating a house. I am rewiring myself. I am getting an electrician to install a new consumer unit & test all my work. I'm looking...
Replies
20
Views
3K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
My Champion generator is set up (according to the manual) as having a floating neutral. The plan was to run a 16A commando hook up cable from the...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock