Hello All, been to price a job up yesterday in a bungalow.. New DB required due to the plumber wanting RCD fuseboard to fit bathroom suite...... (Alarm Bells)
Start by checking the Main Bonding. Water 10mm Gas 4mm. then move onto the board itself. Remove cover and no CPC to lights, therefore a IR test beetween n&e at 250v is done.. 67.9 m oAM for sockets and immersion heater. then after disconnecting all loads on lights IR on l&n to lights and 34.7 m oams. all fine.. and no dreaded nuturals but only one lighting circuit.
Anyway.. Customer advised I would recommend a lights have CPC installed however due to the run it would be false economy to run just a 4mm cpc therefore twin and earth would be the most feasible option. this option declined though as was told the lights work therefore not nessessary..
Anyway.. Cheapest option.. New Db, 10mm bond to gas (10m Run 30min job due to run), Meter Tails and change class one fittings (x2) £260.. With Cert
Apparently that way too expensive. What would you guys charge?
Start by checking the Main Bonding. Water 10mm Gas 4mm. then move onto the board itself. Remove cover and no CPC to lights, therefore a IR test beetween n&e at 250v is done.. 67.9 m oAM for sockets and immersion heater. then after disconnecting all loads on lights IR on l&n to lights and 34.7 m oams. all fine.. and no dreaded nuturals but only one lighting circuit.
Anyway.. Customer advised I would recommend a lights have CPC installed however due to the run it would be false economy to run just a 4mm cpc therefore twin and earth would be the most feasible option. this option declined though as was told the lights work therefore not nessessary..
Anyway.. Cheapest option.. New Db, 10mm bond to gas (10m Run 30min job due to run), Meter Tails and change class one fittings (x2) £260.. With Cert
Apparently that way too expensive. What would you guys charge?