Without ever having seen the machine, I think an element is the most likely cause, in which case the fuse might have to be large enough that it won't reliably co-ordinate with the MCB.

One strategy that bypasses further troubleshooting and might or might not be economical would be to change the elements and any other likely troublemakers and give the machine back to the customer in the knowledge that there's a 75% chance you've removed the fault, despite having no proof of which part it was in. A lot of amateurs think they can fix vintage electronics this way - replace all 100 capacitors and hope - although it tends to add more faults than it removes. In the hands of someone who knows the machines, a shotgun repair can be worth a try when normal faultfinding runs out of enthusiasm.
 
Without ever having seen the machine, I think an element is the most likely cause, in which case the fuse might have to be large enough that it won't reliably co-ordinate with the MCB.

So one could put low ampage fuses which would discriminate with the 32B mcb in all the sub-systems' lines bar the one(s) with high ampage elements......
 
Marconi - I really like that idea, it's brilliant to be fair.
A lot of other manufacturers use a similar method themselves factory standard, the pcb / motor have inline waterproof glass fuse holders. I'm a bit embarrassed the idea has never come to me myself in the past!

I've measured peak current with my fluke 325.
The machine itself isn't anywhere near vintage, it's about 3 years old and is the flagship model of that brand, think it was around 12k when new. Finding a wiring diagram might take me a few days, they don't even have a UK office apparently so I'll have to reach out to one of their distributors to get the schematic.
[automerge]1570640489[/automerge]
Lucien nunes - if it was a run of the mill low end machine I would start swapping out likely culprit components as I have done in the past with intermittent electrical issues, reason I can't with this job is that the customer will almost definitely not want to spend money on bits that just my be faulty, it's such a niche machine that prices are horrendous, there are 15 solenoids inside that are 3 figures each, not priced an element or pcb for it but at a guess I'd say 250 for an element and maybe a grand for the pcb, if he's reluctant to pay a spark to check his supply I don't think he's going to green light the best guess method
 
Last edited:
Does a maximum current of 26A tie in with the total wattage of the heating elements? 26 x 240 = 6.240kW?

What does the specification plate say for power, current and operating voltage?

Ask the client to tell you what the mcbs are for and their ratings to the left and right of the machine's mcb. Is the CU which contains the mcb in a place with a hot ambient temperature with no air flow? Is it a plastic CU? Mcbs often require de-rating for temperature and 'grouping' (- the previous question about what is left and right.)

Are there times in the cycle of producing an espresso when the heating element(s) and a compressor motor are started at the same time?

Is the cup warmer element on constantly or cycled by a thermostat?

Does the machine contain an electromagnetic interference filter at the point the power cord enters?

Does the machine have a work light for the barista to see what he is doing? Is this light fused or only protected by the external mcb? What type of lamp is used - cfl, LV LED, mains LED, LV halogen, LV filament, mains filament?
 
Last edited:
Without ever having seen the machine, I think an element is the most likely cause, in which case the fuse might have to be large enough that it won't reliably co-ordinate with the MCB.

One strategy that bypasses further troubleshooting and might or might not be economical would be to change the elements and any other likely troublemakers and give the machine back to the customer in the knowledge that there's a 75% chance you've removed the fault, despite having no proof of which part it was in. A lot of amateurs think they can fix vintage electronics this way - replace all 100 capacitors and hope - although it tends to add more faults than it removes. In the hands of someone who knows the machines, a shotgun repair can be worth a try when normal faultfinding runs out of enthusiasm.
Was thinking similar, could be an element thats intermittently faulting to earth.

Cant see there being much else there that could handle the fault current and not show signs of damage.

Could it be the bench testing never stressed the elements in the same way real service duties do?
 
The 26A falls within what the machine spec documents. Funny thing with the coffee industry is dataplates on the equipment always tend to have a generous margin of error, a machine badged up at 6kw may only work out on paper too say 5.2kw at full whack however the spec sheet for this machine states 5300 - 7000w.

We have a training room in our place where our baristas hold training sessions for our customers and their staff, the machine has been installed in there with numerous training sessions being done on it where coffees are made continuously for hours on end. I did this to make as real world use as possible due to the issue of bench testing not being as strenuous as real world use.

Essentially the way this machine work is this ...
There are 2 handles where you can make coffee, we call these 'group's. Each group has it's own small boiler with an element and temp stat, so each group has independent temp control, eg left group can be 95C and right can be 92C (don't ask why, it's a coffee thing!) There is also one large boiler with an element in to generate steam and hot water for tea, this is about 70% water and 30% gap for steam to fill, a temp stat will watch the temp of the water, if we ser the machine to produce 1bar of steam it uses a PID system to watch the temp of the water (under steam pressure) and calculate how hot to keep it to maintain steam pressure (~120C under pressure will generate 1bar)

All temperatures are polled constantly and a triac on the pcb will pulse the elements constantly to maintain temperatures.

When a coffee is being made, the push of the button will power a couple of coils on solenoids to allow water to flow out of boiler and through the coffee, the pump also kicks in and boosts water pressure to 9bar.

Since the elements are always pulsing, the pump always runs in conjunction with the elements and one of more powered coil.

The pcb is always powered to run the machine screens and circuitry.

This machine has 3 touch screen panels which are similar to that on your phone, it also has tons of pretty lights, all are LED.

The cup warming element is 240v and also has a temp stat, off / 25% / 50% / 75% and 100% are selectable on the touch screen and this is also monitored by the board and pulsed with a triac
 
Last edited:
I was thinking about replacing the parts at your cost, not the customer's, but it seems that would be a bit expensive unless you really want to keep him on side.

It takes a reasonable size triac to repeatedly knock out a B32 without itself turning from a semiconductor into simply a conductor. Even something like a BTA40 that would switch the total load of the machine only stands up to maybe 1000A²s of fuse let-through, e.g. an F16 HRC. I've no idea what triacs are fitted to the coffee machine but they shed a slightly different light on my 'probably an element,' unless you normally find that the triacs do survive an element short.

I am beginning to wonder if the customer's report was correct, that the MCB tripped when the switch was operated. It is so much less likely than just the RCD tripping, especially in the absence of any installation IR test results.

In the meantime, your testing is obviously not representative. Why not bring the machine along to our workshop. Show us how to use it, give us a good supply of coffee and we'll test it to the best of our electrical abilities. If we ever find the fault, we'll let you know.
 
Last edited:
Ndagger: Thank you for your post. When you add together the power rating of the group elements and the water tank element what figure do you arrive at? Actually I'd really like to know the power of the individual elements as well. Then what is the power of the cup warmer element and the kW/hp of the compressor motor?

Am I picking up correctly that in your workshop (fed by 32A type C)and then when worked hard in the training centre (fed by what size/type of mcb??) for baristas you have not experienced a problem with tripping? If so, then the setting of the machine in the clients premises may well be relevant hence my additional line of investigation about the mcb being derated by temp perhaps?

What does the manufacturer say about type and size of mcb for the machine?

Measure the mains voltage in your workshop and also at the client's next time you visit.

Would you know if the triacs are switched at zero-crossing or phase angle? And lastly, when you say triacs do you mean such devices in a module called a solid state switch/relay which is a little block with 4 terminals, two for load and two for control? If they are SS switches are they random or zero-crossing turn on? If you sent me details I can look them up.

I am wondering - in the absence of information - if the total installed heating power is greater than 6.4kW but triac based heater control technology is limiting the machine's consumption to circa 6.4kW. Maybe there is some spurious triggering of triacs causing an excessive over current great enough to trip the 32B mcb (already hot or de-rated or both?).

A quality of electricity supply problem at the clients causing the spurious triggering? - fast dV/dt of the line -neutral voltage can if not filtered cause triacs which are not gated on nevertheless to be turned on and in your case at the 'wrong time'.
 
Last edited:
Lucian nunes - coffee we've got, by the tonne! Not sure when I'll be passing through London next though but if I do I'll throw the machine in the van!

Marconi - don't have all the answers to hand now but if I get a chance tomorrow I'll get the panels off the machine and note down element wattages and motor rating. This machine doesn't use SSR's (some do though) this uses heatsink mounted triacs, will have to double check part numbers from the package but a lot of machines use tic253 (off top of my head) or similar. The coffee boiler elements are a lot smaller than the steam element, the steam element in most machines have 3 loops, 3 triacs outputting live to each loop. If we ever have an element break down and go short you can get by until a replacement is ordered by disconnecting the line and neutral to the short loop and just running on 2 loops, takes a little longer to heat up in the morning but not normally much of an issue.

Our workshop and training room both use type C 32A mcbs
 
Any scope for slop tray misfortunes , in customer situ is machine spot on level.
( We had a free machine -that shut off if slops bucket got full. )
Is there a night shift on with no machine access ? ... a method was devised to empty slop bucket by our night shift !
Plenty of water users ?..it leaves little residue !
(may be way off - throwing random thoughts in the mix)
Basic thought .. spilled hot water -somewhere peculiar-triggers RCD.
(other differences with install , mech shock thru water feed)
 
Last edited:
Ndagger: You mentioned the espresso machine is on one rccd of a splitboard. If, as I am exploring, the over current is as a result of spurious triggering of the triacs because of a brief high rate of change of L-N voltage aka voltage transient - say when fridges or freezers start or other motorised equipment - causing too many elements to be momentarily energised which causes a current which exceeds the surge capability of a type B mcb - what one might do is:

1a. Move the mcb for the machine to the other rccb to see if that makes a difference - simple and easy to try.

1b. Change mcb to a type C if wiring and installation method allows - an electrician to confirm.

2. Buy a low pass power line filter and wire it into the mains supply to the machine which would filter out the voltage transients. A suitable power line filter is I think - so don't buy yet - this one:

FN2010-30-08 | Schaffner FN2010 Series 30A 250 V ac 0 → 400Hz Chassis Mount EMI Filter, with Stud Terminals | RS Components - https://uk.rs-online.com/web/p/power-line-filters/1705188/

This would need an enclosure, holes, packing glands and wiring in. Easy to do with some skill with electrical components.

It could be that the machine's own EMI filter has failed allowing these voltage transients to trouble the triacs so this component could be change before buying the LP filter.

I am wondering if there is indeed nothing wrong with the machine. Rather it is reacting to unusual voltage transients on the wiring at the clients. The report that the machine has tripped the mcb immediately on power up and also when idle is interesting.

It would also be worthwhile tightening up all connections L, N and E back as far as the meter to ensure loose connections are are not aggravating the situation and also the other final circuits at the CU.

A bit scatter-gun 'cos I am being nagged to take my wife somewhere now - also check that the temperature sensors are screened and properly connected in case their cabling is allowing spurious signals to be picked-up.
 
Last edited:
I've been out all day on call outs so haven't had chance to get any ratings off of the machine but should have a hour free in the morning.

Regarding your suggestions,
1a. I've suggested moving the coffee machine mcb from the left rccb to the right several weeks ago when I thought it could be a accumulation of leakage from other circuits, whilst he hasn't explicitly said yes he will get this done I think he will arrange for that to be done because it's a quick cheap job.

1b. In my last email I did point out that on my type C breaker it hasn't tripped and would recommend he change from type B to c due to the nature of the machine connected to it. He did agree to get this done but also said that as the machine trips during boot up sequence when no elements are in circuit it won't make a difference

2. I have thought about this but based on his sequence of events have put the triacs to the back of my mind for now, he said the machine trips immediately when the rocker makes. This machine is a lot like a computer when it turns on, it displays a lot of info on screen like software rev, a splash screen and other pointless stuff. It takes a solid 90seconds for the "home screen" to be shown and at this point the elements, cup warmer and solenoids start to be energised. I'm awaiting info from the manufacturer on what happens and at what points during this boot up procedure. My understanding is as this machine is computer controlled, for the first 90 seconds after switch on, the only parts energised are the rocker and the pcb. Once booted up the pcb then energizes other parts of the machine with triacs and standard relays but have asked for a flow chart of the boot up procedure from the manufacturer to see exactly what happens behind the black screen of bootup.

And also the first time I returned the machine after not finding a fault in my workshop I thought the original installer may have not tightened one or more terminals in the commando socket and a loose wire may have caused the trip under load so upon return I checked all connections in the socket for tightness, all was fine but haven't checked any terminals in the CU
 
Does the unit have any obvious mains input filter , (separate from pcb)
(also a thorough inspect of mains input cable restraint (if applicable))
Have you done any earth continuity testing
-of kit miss behaving with more than a few mA ?
(like an MFT testers 200mA)
(are any relays involved in initial boot up sequence ?.. as others mentioned L-N path )
.. Monitor supply volts at customers premises as it boots .. (via a commando fly lead ?)
 
Last edited:
Only made it into the workshop for half an hour today but made getting a few snaps of it a priority.
Didn't manage to get snaps of the elements in the coffee boilers as they take a hell of a lot of disassembly to get too but I got the boards, filter, transformer, steam element, one of the solenoid coils (The other 14 are same coil) big black transformer and the motor/pump

Not very detailed snaps I know but time was short, lots of breakdowns today!
IMG-20191011-WA0010.jpg
IMG-20191011-WA0011.jpg
IMG-20191011-WA0008.jpg
IMG-20191011-WA0007.jpg
IMG-20191011-WA0004.jpg
IMG-20191011-WA0005.jpg
IMG-20191011-WA0006.jpg
IMG-20191011-WA0002.jpg
IMG-20191011-WA0003.jpg
IMG-20191011-WA0000.jpg

[automerge]1570822667[/automerge]
IMG-20191011-WA0001.jpg


The red flat element in one of the pics above is a cup warming element, the top panel of the machine is 2 halves, each half has one of these elements on it so there are 2 x what you can see in the pic
 

Reply to Tripping mcb and rccb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
2K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
570
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi, I moved home a few months ago and the electrics RCD keep tripping. Sometimes it will happen every few days and sometimes will be fine for a...
Replies
86
Views
7K
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
Replies
3
Views
732

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock