Hi I'm fairly new to the forum and have a situation I've never came across before. I visited a customers house to quote for a new consumer unit, the existing installation is a wylex pop out MCB board metal clad with a 100 mA RCD main switch with the supply being TT. The earth rod is not visible as a clever building firm built an extension over it, I got an RA measurement in the region of 46ohm. The confusion comes because the supply cable has a lead sheath with earth clamp integrated, I have measured ZE here and got 0.38 which so is providing a perfectly good earth and miles better than the current non accessible TT system. I just wondered if anyone could shed any light as to why there is an earth rod in use if there is a perfectly good earth provided by the supply cable. The owner of the property has always known it to be a TT system. Would it be wise to contact the DNO to ask permission to use the supply cable as the main earth converting it from a TT to TN-S.