I personally wouldn't run the load through timers, I would always use a heavier rated contactor to do the switching, this limits costs when elements fail etc as mentioned in my previous post and also heavier rated contactors have a higher chance of handling a fault current without consequence, it is up to you at the end of the day but unless you have different time requirements for the storage heaters then you only need 1 timer otherwise your just creating more work having to program 2 up the same.
 
If i will buy one timer it must be two channels, right? Then two contractors lets say 20A each, connect all three units will take some time as well. Resistive load in timer I am going to buy is 3.6kW and bigger storage heater is 3.3 so it is still 10% marigin.
 
No your timer controls your contactor why do you need 2 separate ones you can do it by 1 timer controlling a 4pole contactor with your 2 circuits controlled by it but I would suggest having 2 contactors so if one fails you have redundancy and heating still.
 

Reply to Two storage heaters and supply. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
Replies
4
Views
803
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
213
Evening Gents just after a bit of advice and what would you do differently. I have wired up 3 kw heaters in 4mm tuff cable (40 meter distance...
Replies
2
Views
281
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
927
Until last week I had a dual tariff electricity supply with a cheaper overnight tariff. This was good for the storage heating, but now the storage...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top