golfpaul

Hello.

Been asked to add bonding to gas, as British Gas has advised customer gas has no bonding.




Gas meter shows no signs of bonding, cannot see bonding to water either.




They have a shower cu which has a 10mm2 earth to it from the main earthing terminal - no other earth cables leave the MET which leads me to believe that neither gas or water are bonded...however:


With this 10mm2 from the shower connected to the MET, i get 0.00 to gas and 0.00 to water.


With the 10mm2 disconnected, i get a reading of 80v, and tester will not continue with continuity test.


There is a clamp of some sort near the stoptap, with bare cable running through the garage, where it appears to be broken in parts.




Does the gas and water need bonding, seeing as though i get a 0.00 with the shower cu 10mm2 connected to the MET.
And w
hy do i get 80v on shower cu 10mm2?

Ta.
 
yes... gas and water need bonding. that's only part of it. what a bloody abortion.
 

Attachments

  • 292900_ts.jpg
    66.5 KB · Views: 266
Hi,

I usually get into trouble when I mention Bonding on here, But this is my take on it anyway.
You say there is no evidence of any Bonding, but you get a reading to the MET from the Gas/Water pipes. Are they extraneous, that's the question you need to answer.
The reading you are getting is probally where there is an earth connection to a Boiler or Immersion , or something similar; and as we all know Earthing is not Bonding- they have different functions.

Finally, that set up in your picture looks a bit of a mess.

Regards.
 
a bit of a mess? it's a total shambles. a 5 year old could have done better. @OP. do the bonding as in BS7671, then sort that rat's nest out.
 
tin hats wont save the OP from a right royal flaming on this query.

the gas pipe entering the house is metal yes ?

if it was , i wouldnt be messing around with continuity tests looking for some excuse to just leave it like it is..

and the piddling bit of old earth wire in the last photo doesnt look like 10 or even 6mm to me.

course it bloody needs bonding , cant believe theres any doubt or discussion.
 
Gas meter shows no signs of bonding, cannot see bonding to water either.


Does the gas and water need bonding
 

Attachments

  • flabbergasted.jpg
    32 KB · Views: 160
Thanks all!!

I was more unsure about the reading despite no visible bonding being present - and the voltage indicated.

Thanks for the tin hat MDJ
 
Maybe just how I've read this, also can't see the pic too well but I'm wondering. ..
You say no other wires coming from met other than 10mm to shower cu?
Anything going to the main CU???
 
Most likely a meter reader or a BG worker touting for business!!!

My next door neighbour has just had his gas meter moved and they reconnected the bond to the new position, it was fitted that good that the clamp slid down the pipe and the cable dropped out. They had cut the cable as the meter was nearer the CU and in doing so the crimp was no more and they bodged the connection !!
 
Eeeewwwwwwwwww. SEZ ME SITTING HERE WITH A REALLY NICE OLD PECULIER.
 
I thought that may wake you up lol, I am drinking water, can't have alcohol unfortunately, and I have several pints of westons in the fridge as well, gasp!!
 
can't knock weston's. the real ale version of cider. how come no alcohol? don't say doctor's orders. same doctors prescribed thalidomide.
 
Yes, I cut myself to ribbons, My balls ached for days, whoops sorry you mean my beard? yep tried it and it is fine if my face is hot and I use shaving gel, nice bit of kit.
 
Well i don't know what this AHJ is or what it's saying, but if you have a gas main coming into the property in a metal pipe, then it NEEDS bonding!! And if you don't know why, you shouldn't be playing around with electrical work in the first place!!
 
That's not true it is not needed And it could arc the metal gas pipe make a hole in it and cause an explosion

Come on, now you're just taking the pee!! lol!! You have just got to be a 17 day whizzer, or even one of these 5 day whizz kids someone mentioned the other day!! Your statement would be funny if it wasn't so bloody dangerous. For gods sake and your own, find another job, electric's isn't a game you should be playing with, especially in other peoples homes!!
 
Is a term for inspection. Who says you have to bond the gas pipe .
A very simple test will tell you whether the gas pipe needs to be bonded or not. My money is on it needing it, they usually do. Do you know how to carry out this test?
That's not true it is not needed And it could arc the metal gas pipe make a hole in it and cause an explosion
That is so unlikely as to be ridiculous mate, just about every building in this country which has a metal gas main entering it will have bonding to it and those that don't probably need it. If you think that this is a risk please explain where this information comes from so we can debate it.
Do you actually know the reason why services are equipotentially bonded or is it something that we do just for ****s and giggles so that we can waste some of our customers' money?
 
That's not true it is not needed And it could arc the metal gas pipe make a hole in it and cause an explosion
Thinking about this and it has to be a wind up, no one claiming to be electrically qualified, even at the most basic level of 5 week wondery could believe this.
Surely?
 
Thinking about this and it has to be a wind up, no one claiming to be electrically qualified, even at the most basic level of 5 week wondery could believe this.
Surely?

I was thinking the same thing after i'd posted. But then again nothing surprises me anymore with these wannabe chancers....
 

Reply to Unsure about main bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
952
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
434
Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
956
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
433
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top