Discuss Upgrade tails on CU replacement? in the UK Electrical Forum area at ElectriciansForums.net

Another think to consider - Did you upgrade the main earth conductor from the MET?
It was/is common for 16mm tails to have a 10mm earth, but for PME I believe the regs state it must be 16mm.

If it's TN-S then maybe have the calculation ready if you are asked - or say that you've done it, with a confident look!
[automerge]1600721255[/automerge]

Wonder how long it will be before all the Screwfix £70 Dual RCD boards will be Type A?
The regulations do not state that you must have a 16 mm earthing conductor, it can be sized by calculation, regardless of the line conductor but if pme conditions apply , needs to be at least 10 mm( domestically speaking)
 
The regulations do not state that you must have a 16 mm earthing conductor, it can be sized by calculation, regardless of the line conductor but if pme conditions apply , needs to be at least 10 mm( domestically speaking)

I always thought it was 16mm to avoid the need for mechanical protection
 
I always thought it was 16mm to avoid the need for mechanical protection
No, it’s sized upon table 54.7 or by the adiabatic equation.
If buried etc then other considerations for CSA apply.
New installations like new build houses, the DNO stipulate 25 mm tails and a 16mm earthing conductor.
 
Last edited:
Hi. I have my NAPIT first assessment soon and I replaced a CU in a house which has 16mm2 consumer tails in place. I did not upgrade the tails to 25mm2, so my question is should I have upgraded them or am I allowed to leave the existing tails in place?
I do not know the rating of the DNO cut-out fuse
Yes the cut-out does have 100A stamped on the fuse carrier but that means nothing
Installation is 25 years old

Thanks
[automerge]1600593380[/automerge]

Also it was a Lewden RCBO board and I brought the cables through the knockout in the rear, am I required to use fire sealant in the rear section?
Hi Andrew,

Your assessor may or may not have a moan about the 16mm tails, each assessor seems to be different. Don't worry though, absolute worst case scenario is that you will have to upgrade to 25mm and that is unlikely.

I assess if 16mm tails need upgrading by looking at max demand and seeing if that is in excess of the CCC of 16mm cable. Also I check to see if it meets regulation 434.5.2, i.e protection of tails against fault current.

You could even show the above to the assessor as it is written in Best Practise Guide number 1 (Replacing a consumer unit) issue 4, section 5.1 note 4 as follows:

"16 mm² meter tails with a 100 A cut-out fuse could be adequate if the maximum demand of the installation (taking into account diversity and load profile) does not exceed the current-carrying capacity of the tails, and also provided that the requirements of Regulation 434.5.2 for protection of the tails against fault current are met."

You'll have to brush up on K² S² > I²t just in case he asks you to prove it meets the regulation though :D

Good luck :)
 
Last edited:
The regulations do not state that you must have a 16 mm earthing conductor, it can be sized by calculation, regardless of the line conductor but if pme conditions apply , needs to be at least 10 mm( domestically speaking)
Agreed that it can be calculated. I thought there used to be a specific PME reg, but apparently not currently - that is only when applying to bonding conductors.

Table 54.7 says that for a cross sectional area of Line conductor S up to and including 16, the protective conductor must also be S (if same material), so if not calculating and using that table 10mm earth would only be allowed on 10mm tails, and 16mm required on 16mm tails (then 16mm until S > 35)
 
Agreed that it can be calculated. I thought there used to be a specific PME reg, but apparently not currently - that is only when applying to bonding conductors.

Table 54.7 says that for a cross sectional area of Line conductor S up to and including 16, the protective conductor must also be S (if same material), so if not calculating and using that table 10mm earth would only be allowed on 10mm tails, and 16mm required on 16mm tails (then 16mm until S > 35)
Yes by design however if it’s existing there’s very little chance that a 10 mm earthing conductor will not satisfy the adiabatic so does not require to be changed.
 
Thank
Hi Andrew,

Your assessor may or may not have a moan about the 16mm tails, each assessor seems to be different. Don't worry though, absolute worst case scenario is that you will have to upgrade to 25mm and that is unlikely.

I assess if 16mm tails need upgrading by looking at max demand and seeing if that is in excess of the CCC of 16mm cable. Also I check to see if it meets regulation 434.5.2, i.e protection of tails against fault current.

You could even show the above to the assessor as it is written in Best Practise Guide number 1 (Replacing a consumer unit) issue 4, section 5.1 note 4 as follows:

"16 mm² meter tails with a 100 A cut-out fuse could be adequate if the maximum demand of the installation (taking into account diversity and load profile) does not exceed the current-carrying capacity of the tails, and also provided that the requirements of Regulation 434.5.2 for protection of the tails against fault current are met."

You'll have to brush up on K² S² > I²t just in case he asks you to prove it meets the regulation though :D

Good luck :)
Hi Andrew,

Your assessor may or may not have a moan about the 16mm tails, each assessor seems to be different. Don't worry though, absolute worst case scenario is that you will have to upgrade to 25mm and that is unlikely.

I assess if 16mm tails need upgrading by looking at max demand and seeing if that is in excess of the CCC of 16mm cable. Also I check to see if it meets regulation 434.5.2, i.e protection of tails against fault current.

You could even show the above to the assessor as it is written in Best Practise Guide number 1 (Replacing a consumer unit) issue 4, section 5.1 note 4 as follows:

"16 mm² meter tails with a 100 A cut-out fuse could be adequate if the maximum demand of the installation (taking into account diversity and load profile) does not exceed the current-carrying capacity of the tails, and also provided that the requirements of Regulation 434.5.2 for protection of the tails against fault current are met."

You'll have to brush up on K² S² > I²t just in case he asks you to prove it meets the regulation though :D

Good luck :)
Thanks for your reply. WPD are coming out today to confirm the type/rating of the cut-out fuse, which he suggested on the phone that they never fit 100A.
The tails have been in situ since 1995 and there are no signs of thermal damage, also I have examined with my FLIR E4 camera for hot spots. Maximum demand is around 50A
Cheers
 

Reply to Upgrade tails on CU replacement? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
543
Was helping a friend out and changing their CU which had a date stamp from 1990. Good quality Merlin-Gerin unit and a nice job originally. They...
Replies
7
Views
789
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock