Had to change a bathroom fan at the weekend for someone and they wanted it to be on a timer, but couldnt as the cable was buried in the wall and wouldn't move etc..

the cable that fed it was a three core flex, I the earth was not being used anyway due to the load on the end etc.

I know you are not meant to use the CPC as a live conductor, but if its flex and the same CSA and you were to correctly identify it with brown etc, would it have then been acceptable?

I didn't do it, but it made me think, oh i so could have used it, but it just seemed wrong. I can understand why you wouldn't do it in twin and earth, but surely where its flex or all conductors are the same CSA and have their own sheathing on them inside the outer, would it have been acceptable or not?

I am going to say not on the basis CPC is CPC and nothing else, any thoughts would been welcomed.
 
Simonslimline and uksparks feel to buy a copy of this book and read it sometime rather than listen to the NIC or any other CPS.

Regs.jpg

- - - Updated - - -

Yes i am aware of that... i was simply mentioning what i had read :)

I read in the beano you can fall along way off a high cliff and walk away unhurt, does it make it true?
 
I am pretty sure the NIC mentioned this a while ago and said you can. They do seem to make it up as they see fit though.

Also i am fairly sure that you should not bury flex in a wall!

Is there a specific reg for this??? Daz
 
Check your regulations under cable Identy 514.4.2

Theoretically yes its just a colour but a big no no for various reasons.
 
I am trainee and do own BS7671, if you read my post it does say that the NIC make it up as they see fit. I mentioned it only as i remember reading about it a while back.

Simonslimline and uksparks feel to buy a copy of this book and read it sometime rather than listen to the NIC or any other CPS.

View attachment 23389

- - - Updated - - -



I read in the beano you can fall along way off a high cliff and walk away unhurt, does it make it true?
 
as long as the fan was classII and there was no alternative, i might be tempted.
 
I am trainee and do own BS7671, if you read my post it does say that the NIC make it up as they see fit. I mentioned it only as i remember reading about it a while back.


Well then you need to read it, threads like this will help you understand it more. Only say something you have read by providing a link to it to prove your point.
 
I remember a story going round a while back (90s) about a plumber who cut into an existing boiler wiring flex that had cpc as live - can't remember details but he connected the cpc to earth term somewhere in his jb and result was fatal shock for homeowner off the kitchen sink.
 
I remember a story going round a while back (90s) about a plumber who cut into an existing boiler wiring flex that had cpc as live - can't remember details but he connected the cpc to earth term somewhere in his jb and result was fatal shock for homeowner off the kitchen sink.

i can only see that happening if there was no earthing on the installation.
 
Bear in mind he would have used this 'earth' terminal to earth whatever he was installing (new boiler/whatever) making it live and anything metallically connected to it (eg copper pipes to sink)

As I say I don't remember details but there could have been other factors contributing.
 
then if the installation was earthed, the OCPD would have operated as soon as he'd connected it to a line conductor.
 
Tel...
The way I understood it the plumber thought that the cpc in the flex was his earthing source so everything he did from that point on was isolated from the actual earth (no real cpc present in his jointing box) - no reason for OCPD to operate
 
I remember a story going round a while back (90s) about a plumber who cut into an existing boiler wiring flex that had cpc as live - can't remember details but he connected the cpc to earth term somewhere in his jb and result was fatal shock for homeowner off the kitchen sink.

It was in the papers in the nineties as you say. the plumber got time for it.
 
used to come across this when doing boiler upgrade work on the s-plan and y-plan systems, the way I see it is that the CPC is there to protect the cable aswell, bad practice.
 
I 've had another think on this and I'm almost certain it was an electrician, not a plumber, who was at fault.
When he was questioned in court he couldn't even say where the consumer unit was

Probably been a Electrical Trainee "electrician" who did it then ............. hang-on, did they do Electrical Trainee courses in the 90's?
 
i would have had no problem using that flex , brown sleeving on both ends whats the problem , common sense over rules the the regs sometimes , tin hat firmly on
 
I have no idea who wrote that, but the reg they quoted applies to PEN conductors. So even the diagram used is a load of baloney.

Must a typo - I think they mean 514.4.2. Daz

- - - Updated - - -

The diagram doesn't show a PEN conductor.
 
as long as the fan was classII and there was no alternative, i might be tempted.

Yes Class II, tempting isn't it. i didn't though as I felt it was just wrong. The problem was the flex was buried in the wall and I really wanted to swap it for a bit of three core, but though hmmm I could use that CPC as its not being used... It was a conductor like the others, so its not like it didnt have any insulation or a smaller CSA.
 
It doesn't. If it's over sleeved at the end than its ok.

Unless it's a single core cable which can not be sleeved over.


But as darkwood says it's not good practice...
Thats not the way I read the reg, it says green and yellow cables throughout their length shall only be used as a protective conductor, the oversleeve bit is when you mark the ends with a blue indication for PEN conductors.
 
Problem is when, as mentioned, someone taps into a cable, sees green & yeller, assumes its a cpc.....etc

That's where I was going with it, I know If I cut into a cable and i saw a green / yellow, I probably wouldn't give it any thought and think, yep that's the earth. I think its a good idea to use a CPC as a CPC only and nothing else.
 
I think if you start using whats really seen to be an earth throughout its length as a live conductor, you are kind of cutting corners in a way and your standards (if you have any) will probably start going down hill, personally I would rather do the right thing and tell the customer, that's going to cost you, you need a new bit of cable.
 
The two regs in question are here, in case anyone hasn't got the regs with them:

514.4.2 Protective conductor

The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor

and this combination shall not be used for any other purpose. In this combination one of the colours shall cover at

least 30 % and at most 70 % of the surface being coloured, while the other colour shall cover the remainder of the

surface.

Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective

conductor and shall not be overmarked at their terminations, except as permitted by Regulation 514.4.3.

A bare conductor or busbar used as a protective conductor shall be identified, where necessary, by equal green-andyellow

stripes, each not less than 15 mm and not more than 100 mm wide, close together, either throughout the

length of the conductor or in each compartment and unit and at each accessible position.

514.4.3 PEN conductor

A PEN conductor shall, when insulated, be marked by one of the following methods:

(i) Green-and-yellow throughout its length with, in addition, blue markings at the terminations

(ii) Blue throughout its length with, in addition, green-and-yellow markings at the terminations.
 
I think its rather laughable that the NICEIC have actually condoned it in an article.
Yes they are trying to re write the regs. Lets look at this from another aspect, where in the regs does it say it is acceptable to use a green and yellow conductor for a live conductor even if the conductor is marked? It won't, it just won't.
 
Must admit, I've done it.....but it was on 400w sons 30 ft in the air, before we had internal photcells. The photocells had to be fitted to the brackets with 3 core flex from the fitting, about a foot long.

Shoot me for that you word for worders.......NIC ban on the way, no doubt!!!:cowboy:
 
Must admit, I've done it.....but it was on 400w sons 30 ft in the air, before we had internal photcells. They had to be fitted to the brackets with 3 core flex from the fitting, about a foot long.

Shoot me for that you word for worders.......NIC ban on the way, no doubt!!!:cowboy:
Your not the only one, I have seen it done myself, however it doesn't make it right these days, I have seen it in the past.
 
But the cable is a 3 core flex not a single core.

The electrician/plumber/competent person !! who cut into the cable feeding the boiler would have realised his mistake if he had tested the modified circuit.
 
Your not the only one, I have seen it done myself, however it doesn't make it right these days, I have seen it in the past.

Well, in that situation, up in the air, if they can't weigh up what's what with a foot of flex to a p/cell they deserve everything they get.
 

Reply to Using CPC as live conductor.... ok i know, but... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
639
I see they're introducing a new type of flat twin cable with a sheathed CPC. In my location there's no requirement to sleeve CPC/bonding...
Replies
21
Views
2K
A recent discussion on conduit choice wandered over to pros and cons of the 'conlok' style and a link was posted to one of the Efixx videos in...
Replies
29
Views
4K
Does anyone know what the cable in the picture is called? Or anything about it? Labelling on the outside is “E SPC Electric Cable 600/1000v” Its...
Replies
9
Views
1K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock