339
Evening all,

A job I am on as an aside the customer asked me to have a look at the heating/hot water system as the hot water is not heating up. It is an unvented system with vaillant boiler and combistore cylinder.

Anyway I tested up to the tank stat/cylinder control and found power up to it (terminal 1) but not going through it out to terminal 2 or terminal 3 if I turned the temperature down. So I've called vaillant to check I'm not being daft (always a good chance) and they say no the stat is faulty you need a new one.

Long story short the customer ordered a new stat, I replaced only to find the same problem, I scatched my head and rang vaillant again and they said that's unlucky you must have a 2nd faulty stat....got another one sent and same problem again.

Anyway I bypassed the stat and had the system running fine. Bit of a head banger, have tested across terminals 1, 2 and 3 but nothing. Any thoughts welcome!
 
any thermal cut out device on the stat that's tripped? other thank that you have bypassed the stat and the boiler and the motorized valve has opened so the wiring's ok so looks like you have another faulty or wrong stat
 
What a pipe stat? There is one I'll check it again when I go back next but don't think it's that, the cylinder control has 240v coming in but no going across, the pipe stat is above the cylinder and not directly connected so don't see that it could affect that.
 
What a pipe stat? There is one I'll check it again when I go back next but don't think it's that, the cylinder control has 240v coming in but no going across, the pipe stat is above the cylinder and not directly connected so don't see that it could affect that.

No, the high limit stat in the unvented cylinder controls, also known as a safety cutout.
 
Well, if you have the stat in your hand, turned down and no continuity across NC contacts then that's your problem still. You have already proved system by linking out (assuming you linked out at stat position).
 
Sorry I see what you mean...possibly, would that be somewhere on the cylinder as opposed to being integral to the part that I've changed then?
 

Reply to Vaillant combi store cylinder stat problem in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
1K
i , i have a property to work on which has a programmable room stat upstairs and a programmable roomstat downstairs. S plan system , 2 zones. hot...
Replies
5
Views
409
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
649
Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
467

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock