Hi can any one tell me is it a regulation in a wood cutting workshop or mechanics garage to have vapour proof fluorescent fittings. Do i right it down on a electrical condition report.
Many thanks
 
Electrically any accessory should be suitable for the external influences found in the environment, if you have a woodworking shop where there is a lot of dust then the lighting system should be designed such that the build up of dust does not cause a problem for the electrical equipment.
The decision on whether it would be coded in an EICR would be yours as you have seen the situation.
A mention in a covering letter may be advisable, as a recommendation, that dust proof fittings should be used; if a problem is occurring.
 
  • Like
Reactions: 1 person
Hi can any one tell me is it a regulation in a wood cutting workshop or mechanics garage to have vapour proof fluorescent fittingsBs7671 is never that specific,if you are carrying out EICR's you should have access to Bs7671 and have an understanding of it's contents. Do i right ...write I think you will find it down on a electrical condition report.
Many thanks

.......
 
i prefer to use self-raising flour ecents. is it 100ecents to the euro?
 
A wood cutting workshop or mechanics garage have the possibility of been a zoned area, there should be a drawing of the building detailing any zoned areas, usually just zones 1 or 2. Any electrical equipment in these areas need to be suitable for the environment, ExD or similar.
 
so iss bailing out at 20,000 ft. without a parachute.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Vapour proof flourecent fittings
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
cdmh electrical,
Last reply from
pepparz,
Replies
10
Views
1,150

Advert