Discuss Voltage reading puzzle in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
T
toast
230V single phase supply.
6amp Lighting circuit, T&E 1.0/1.0
Readings
Highest r1+r2=1.72
IR: L-N, L-E, N-E all >299 Mohms
But when energised there is voltage reading across the conductors at the board as follows:
N-E 112V
L-N 107V
L-E 107V
Then at the light fittings:
N-E 127V
L-N 240V (closed circuit)
L-E 7V
The voltage readigns were taken with Line and neutral terminated at MCB and neutral bar respectively but with CPC/Earth not connected at Earth bar.
The circuit does not trip when energised.
Any thoughts of why this is occurring?
Firstly why did you test the voltage with the CPC disconnected?
Secondly, think about what you havent done, and why you are experiencing the problems that you are.
Thirdly think about what you have done again, and why this might stop the circuit from tripping if there is an earth fault!
You should be able to answer your own questions if you think about it.
Cheers..........Howard
There had been a unit swap (not by me) and the installer called me as they had got a belt of the CPC. that is why I tested as I did.
I can only think that it is a polarity problem as I get continuity with earth and IR readings are really good.
But I tested all Perm lives at fittings, so if it polarity must be connected incorrectly within voids or walls.
All other circuits test off fine.
I know without earth connected there will be no earth fault.
where did he get a belt off the cpc? consumer unit end or at the light? if hes changed the CU and the lighting circuit worked fine previously then its something hes done, maybe nicked a cable when screwing the CU up?
Con unit
I was informed reason for unit change was that there had been fusing issues. But the information I have received regarding this, so far is vague.
But if cable nicked, I would expect IR issues!
he sounds like he doesnt have a clue. id be checking everything again, if hes stupid enough to do that god knows what else hes done.
May sound scary but I wasn't there at the time. So don't know the reason behind this, just know that he got a belt, which then led me to testing as I did.
Well that is a fair assumption, I did disconnect all the circuits and reinstalled, without the aid of any pre-planned EIRC and a young family with pregnant mother complaining about the heating and Jeremy Kyle being off.
All other circuits tested off fine.
This is genuinely not a wind up.
Reply to Voltage reading puzzle in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...