went to a house split into 2
the lady had bought it "years before but plugged the kettle into the socket in the living room as she sometimes got a shoch of the kettle in the fitchen also the dimmer switch vibrated when you touched it
the cause
when they rewired and did the downstairs up they tiled the kitchen then put a cupboard around the boiler in the kitchen they drilled through the cable so the fuse must of kept tripping
so the disconnected the mains earth so the whole flat was live ,all metalclad switches and sockets were 230v except the gas cooker thats how she was getting belts in the kitchen when she brushed past that