Anyone know what the ‘standard’ tabulated cable rating is for 6mm rubber in France? Alternatively, put the other way around, what’s the size for a 63/3 sized supply, free air
 
Agreed (here). I’m trying to help a colleague who’s in France and dealing with a poorly installed 63/3 Commando outlet, overheating etc due to being installed in 6mm and getting fobbed off by a local cowboy that it meets French Regs - she’s looking for a Reg argument to tell the venue owners to get it done properly and stop being ripped off.
 
Agreed (here). I’m trying to help a colleague who’s in France and dealing with a poorly installed 63/3 Commando outlet, overheating etc due to being installed in 6mm and getting fobbed off by a local cowboy that it meets French Regs - she’s looking for a Reg argument to tell the venue owners to get it done properly and stop being ripped off.
Show them this Choix de câble domestique - Repère Elec - http://www.repereelec.fr/cables-dom.htm

Needs 16mm if it's pulling over 60a.
 
Last edited by a moderator:
Surely cable doesn't know which country its being installed in so if you can go by the manufacturers instructions for amp rating ?
Different regs though. Like you're not allowed to install ring finals, you're not allowed more than 12 sockets on a radial, etc.
 
Different regs though. Like you're not allowed to install ring finals, you're not allowed more than 12 sockets on a radial, etc.

And remember you need a consumer unit the size of a filing cabinet 😀
 
Like you're not allowed to install ring finals
Again, due to plugs in France not having a fuse.

So often folk don't grasp that is such a fundamental difference between the UK domestic (13A) socket outlets and most of the rest of the world.
 
  • Like
Reactions: pirate and DPG
Again, due to plugs in France not having a fuse.

So often folk don't grasp that is such a fundamental difference between the UK domestic (13A) socket outlets and most of the rest of the world.
It's more likely that it's due to them just being unnecessary imo.

Although the way they do it there, you're allowed so few sockets on a radial run that it actually uses more cable than a ring would use.

In my house i had 1 radial for dining room and front room (12 sockets), 2 radials for the upstairs, cooker feed, hob feed, washing machine feed, dishwasher feed, freezer feed. And my house was small. Needed a 2-tier since you have to leave a certain amount of space in the unit.

Still, i prefer how they do it there, so much of it is much better than here.

I'm still waiting for us to finally come on board and use circular back boxes so we can stop fannying about with cutting in rectangular boxes and just use a big hole saw.
 
Twelve sockets on 2.5mm or Eight sockets on 1.5mm not forgetting no T&E as the earth is not double insulated as singles in Gain would be, my CU was four tier as it was a three phase supply, one tier for incoming and external supply RCD's all four module and three other tiers, one for each phase.

The only problem with circular back box's is that glands don't fit, but like most French electricians they just stuff the gain into the back box, or leave it just short. 😇
 
But presumebly the fresh air / clipped direct rating for any cable will be exactly the same no matter what country to install it
Yeah but that doesn't mean it comes within their regs. 6mm is rated for 40a there in their regs not 47a like here. Their cable is all round profile, i don't know if that makes any difference in terms of temperature etc?
 
Yeah but that doesn't mean it comes within their regs. 6mm is rated for 40a there in their regs not 47a like here. Their cable is all round profile, i don't know if that makes any difference in terms of temperature etc?
Also I believe all their cable needs to be run in plastic conduit as well which may effect how they de-rate their stuff
 
Not quite true, double insulated flexible cable can be used at high level to supply power and lighting too an outhouse or caravan, but not recommended.
 
Also I believe all their cable needs to be run in plastic conduit as well which may effect how they de-rate their stuff
It doesn't have to be, although in most properties it's run inside flexi conduit (the conduit comes pre-wired!) in singles. Their actual cable is colour coded and is actually meant to be run outside but you can also use it inside if you want.
 
Domestic supplies to plugs, lights and white goods has to be run in conduit, it comes either prewired or in rolls with a draw cable.
 
  • Creative
Reactions: swaRRR

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Rockingit

Mentor
Arms
Supporter
~
Joined
Location
Somerset
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Who knows French Regs??!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
16

Advert

Thread statistics

Created
Rockingit,
Last reply from
Mike Johnson,
Replies
16
Views
1,618

Advert