3 circuits, 32A cooker, 32A ring and 6A lighting. The main cut-out fuse is 60A. New meter been fitted within the past year or two and the tails from the meter to fuse board were obviously replaced at the same time. They are 16mm tails. Personally I see no reason to replace them - Am I wrong?!
Hi - the 16mm conductors are rated above the 60A fuse and the load seems quite modest. So it seems fine to me.
Maybe I’m wrong too .