Hi Guys, a little bit of help required. I'm trying to tidy some wiring in the loft above the kitchen. Whoever lived here years ago seemed to do all his wiring with red tape and connector blocks. For some reason (probably to get rid of all the little bits of wire) they have used 4 different pieces of 1.5mm twin and earth from the consumer unit to the boiler. There is a 6amp mcb on the CU and a 3amp fuse and the boiler and there is nothing else on the radial. The question is, I have half a reel of 1.0mm in the garage, can I replace these bits with one piece of 1.0mm or should it be 1.5mm. Thanks in advance for any replies
 
A 1 mm² T&E cable will, so long as it is not buried in insulation and bunched with other circuits, have the current carrying capacity to be safe to use, however as you are changing the capacity of cable the full range of tests for a minor works electrical installation should be undertaken to ensure that the circuit is safe to use.
 
Thank you for that Richard but from what you are saying would it just be easier to change like for like and its only going to cost ÂŁ20-30 with no hassle of getting it tested?
 
Is my memory playing up, or do the regs not call for a minimum 1.5mm for such connections?
 
Thank you for that Richard but from what you are saying would it just be easier to change like for like and its only going to cost ÂŁ20-30 with no hassle of getting it tested?

So you'd change a cable and NOT test it?
 
So you'd change a cable and NOT test it?

as that a full range of tests of the wiring because I have changed the carrying capacity or if I'm changing like for like just test to operate as it should..... I think most people knew what was meant.
 
you replace the cable in it's entirity with 1.5mm. before energising, do your dead tests ( continuity, polarity, IR ) then energise, get your Zs. complete a MWC. job's a go.
 
Is my memory playing up, or do the regs not call for a minimum 1.5mm for such connections?
Yes, power circuits minimum csa 1.5mm² no matter what size the circuit protection, a silly change introduced in amendment 2.
 

Reply to Wiring to boiler from Consumer unit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
In the UK, It is said that the neutral wire is connected to ground/earth wire along the way back to the substation. Ive inherited a setup where...
Replies
4
Views
1K
Hello wise electricians of the world! I am in the UK. Recently we had a water leak which caused some damage in our home, we are currently trying...
Replies
25
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock