Hi All,
Currently in the process of my NIC application. Completed one job and had it signed off. Just installing a socket at home on its own circuit directly under CU. Going through my test results cant understand the difference in readings.
Measured Ze is 0.12
Measured R1+R2 is 0.01
Was expecting a result around 0.13
Instead results keep coming back between 0.19 and 0.22 which I think is quite a bit more than the expected. Bearing in mind its run in 2.5 T+E and the socket it about 6 inches under unit. Anyone any ideas about the difference in readings?
All leads were nulled, each test was done twice as I thought it could of been a dodgy reading. I know its not a huge amount and nothing to worry about but couldnt understand why its so different. Its a megger m/f im using

Got building control coming out tomorrow then it shall be time to book site visit!

Thanks for all the support!

Rob:icon4:
 
The extra impedance is probably due to the RCD, assuming there is one.

Edit: Or that you're using a non trip test for the direct Zs measurement...
 
Last edited by a moderator:
i never find them to be the same when comparing measured and calculated results , always a sligh diffrence, n my opinion .04,and .05 is not much or am i missing something here
 
cheers for the replies! Now I know for next time.
No .04 isnt a lot but when the R1+R2 is only 0.01 it made me wonder if I was doing something wrong.

Thanks again,

Rob
 
the fact that the measured value is different from the calculated value shows that you have measured the values not tried to fudge them. don't worry about it. as said previously, this can be expected.
 

Reply to Ze+(R1+R2) is lower than measured Zs in the Australia area at ElectriciansForums.net

Similar Threads

Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Replies
17
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock