If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Call out to a job,flat with Db protected by 30ma trip as main switch.
Rcd had tripped but not in clients flat,main intake area downstairs.
There I found a 30ma rcd which supplied Db in upstairs flat.
Apparently this as been tripping on a regular basis,& got worst,obviously no discrimination between rcd s,& so,a nuisance.
Did all the correct testing,& installation proved ok,rcd tripping times ok too.
Major concern is that it's a tt system,& there are other rcds in situ,controlling various other supplies.
At main intake a 100 ma time delay rcd is installed,& sometimes this trips,& causes havoc to all.
The flat seems to cause all this once tripped,tried explaining to client the ins & outs,but goes way over the head.
I think I gonna do a runner.
 
Why is it a TT system ? what testing have you done so far.
alot of the time RCD/RCBO's don't trip is that they stick as not tested quarterly
 
Sounds like a new design for the installation is needed, which could be an opportunity. As I read it, there must be a fault somewhere that's setting off the RCDs but it might be tougher than usual to find. If you do carry on with it - perhaps IR test circuits with external lights - I've had a couple of these go bad recently with the seasonal damp (and diy ... ).
 
Why is it a TT system ? what testing have you done so far.
alot of the time RCD/RCBO's don't trip is that they stick as not tested quarterly
No Earth provided by Rec,insulation tests between conductors all fine,times are ok.
 
Sounds like a new design for the installation is needed, which could be an opportunity. As I read it, there must be a fault somewhere that's setting off the RCDs but it might be tougher than usual to find. If you do carry on with it - perhaps IR test circuits with external lights - I've had a couple of these go bad recently with the seasonal damp (and diy ... ).
Cheers exactly what I think,its like your an electrician it's gotta be fixed now !!
This all happened late afternoon today,so most probably go back soon,or someone else's headache.
,cheers,happy new year.
 
I think exactly what Wilko has put above to also if there is a leakage to earth from each flat and landlords but not enough to trip 30mA but together trips 100mA how old is the installation.I would see if supply could be upgraded to PME etc if a earth is provided to the buildings nearby gives a good indication.
 
  • Like
Reactions: Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Funny business
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
cliffed,
Last reply from
Toneyz,
Replies
5
Views
1,162

Advert