Discuss Changes are coming, what do you all think in the UK Electrical Forum area at ElectriciansForums.net
So, ATM if you have PME and have to TT a car charger ..... Then the muppets decide if you have PME you need to have a rod
They just don't know what they are doing or suggesting.
And if it's a 10th floor flat, what then?
That's the question my boss asked, what happens if it's a flat. Do you think the extra cost of having to add an earth rod will put people off having a board change or will more people be looking for a cowboy to do it cheaper
For this reason details will be included in BS 7671:2018 for the installation of arc fault detection devices (AFDDs) to mitigate the risk of fire in final circuits of a fixed installation due to the effect of arc fault currents.
American pressure sales have worked wonders on members of JPEL/64.or is it one American import that is desperately needed?
I was refering to using a ground rod NOT bonding !
I assume you mean that plastic pipes are creating natural installation isolation from earth and nolonger providing a parallel path so it is more so essential to ensure the earth rod if used gives a good reading... you comment was somewhat ambiguous hence my reply :)
Potential Customer has asked me to put a power socket on the outside wall of his garage, what's it for I ask conversationally "its to charge up my hybrid"... PME, so IET Code of practice recommends min 2 by 2.4m rods. Plus get it back to MET. I wish I'd just shut up.
I more or less had to refuse exactly that request recently. It's going to get more common, and especially with hybrids which only need small charge off 13A socket, hard to draw a line against the regs.
There’s a number of issues I have with this particular proposal.
1, This proposal is supposedly in case of a supply Neutral fault, which the DNO’s have a Statutory requirement to maintain and protect consumers if such faults do occur.
Why is the IET proposing another Non Statutory Regulation to offset a breach of Statutory requirements?
2, In the event of any such fault occurring, the installation Earth will effectively become the Neutral.
Is this acceptable?
Are the present Installation Earthing and bonding CSA requirements sufficient?
3, In situations where it is not practicable to install Earth electrodes and perhaps even in situations where it is practicable, should upfront RCD protection also be provided so as to disconnect the supply in the event of a supply Neutral fault?
& This would need to be before MET then wouldn't it? - Thus the property of DNO ?
IETLTP.that is translated...
IET lost the plot.
Agree - If the neutral is lost surely we should isolate the installation not add rods so it can carry on in a busted condition ?
At present if there were a supply Neutral fault, the bonding and extraneous metal pipework would become the Neutral.
This proposal has been introduced as so much of the gas and water supply network has been changed to plastic.
No it would not be the property of the DNO, just as an upfront RCD for a TT Installation would not be the property of the DNO.
I don't see that. Image attached. Surely in PME case, an RCD would need to be before the head so as to be able to pick up on return N current not running in PME N ? - It could still look balanced in the tails.
Hi J, IIUC with an upfront RCD (same position as TT case) the RCD would sense current in L and not N as it's now going back through the rod. And so it'd trip. We would still need a rod (at the PME terminals in your pic) but now we just use it to disconnect the installation rather than put in many rods and try to keep touch voltages down.
But it's not fault current, it's any residual installation neutral return current which is able to lift the MET and all exposed conductive parts. The neutral current is surely still balanced in the tails since it's got to be the same as any live current. (There is no earth fault in the installation during this condition to make it otherwise)
I can see the logic in it to be honest IET have produced guidance notes on this before but NICEIC inspectors would give you a berating for having 2 different earthing arrangements . So when you are asked for earthing arrangement at origin what would you put down TNCS, TT or will there be a new classification code TNCS/TT?
Would you have to install a rcd on tails from the meter before they enter an AMD 3 board rated at 30mA, or would you be able to install an rcd with upto 1A tripping current as it is for a dribution circuit on a TT system? Could you decide to ignore the TT side of it and continue as for TNCS as the TT part would only come into play when DNO lose neutral on their network. I don’t mind as I am on a trusty old TNS supply at the moment lol.
Reply to Changes are coming, what do you all think in the UK Electrical Forum area at ElectriciansForums.net
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...