Hi

I’m thinking of changing an extractor fan (in a WC) to one with a run on/timer. The current set up doesn’t have an isolator, and wiring runs from the light bulb to the fan, which is sited in the ceiling about 18” away. The fan is vented through a flat roof above.

Now, I realise that i’ll need a permanent live and to fit an isolator switch. I’m thinking of doing this:
- to leave existing wiring as is, and take a live feed from a lighting circuit junction box in the attic;
- to install an isolator switch in the permanent feed run, ie in the attic.

I’d rather not have to channel into walls to run a new 3 core cable.

Thanks
 
Hi

I’m thinking of changing an extractor fan (in a WC) to one with a run on/timer. The current set up doesn’t have an isolator, and wiring runs from the light bulb to the fan, which is sited in the ceiling about 18” away. The fan is vented through a flat roof above.

Now, I realise that i’ll need a permanent live and to fit an isolator switch. I’m thinking of doing this:
- to leave existing wiring as is, and take a live feed from a lighting circuit junction box in the attic;
- to install an isolator switch in the permanent feed run, ie in the attic.

I’d rather not have to channel into walls to run a new 3 core cable.

Thanks
Sound like a rubbish plan.
 
Do you not think it would be a good idea to isolate the 'switch live' and 'neutral' as well?
 
Last edited:
or give this guy a job.
49903
 
Hi - just so you know - new regulations from January mean that changing the wiring on a circuit with lights will require an RCD be fitted, if it’s not already. And depending on details, a building works notification (Part P) might also be required as you are doing electrical work in a bathroom. An Electrician can help you with both of these aspects, as well as testing the completed works are safe, just saying :) .
 
That really doesn't sound good at all Daljit, also dangerous because:

1. You could be taking the permanent live (PL) from a different circuit.
2. You will only be isolating the PL not the switch live, so if you do use the isolator switch (i use the term lightly) you would still have a live fan when the light switch was on. Someone who moves in after you could well get an electric shock as they would never suspect that it had been wired so badly.

I realise you are probably trying to safe some money but you really should get an electrician to do this work.
 
Hi - just so you know - new regulations from January mean that changing the wiring on a circuit with lights will require an RCD be fitted, if it’s not already. And depending on details, a building works notification (Part P) might also be required as you are doing electrical work in a bathroom. An Electrician can help you with both of these aspects, as well as testing the completed works are safe, just saying :) .
Hi, WC so no special regs
 
That really doesn't sound good at all Daljit, also dangerous because:

1. You could be taking the permanent live (PL) from a different circuit.
2. You will only be isolating the PL not the switch live, so if you do use the isolator switch (i use the term lightly) you would still have a live fan when the light switch was on. Someone who moves in after you could well get an electric shock as they would never suspect that it had been wired so badly.

I realise you are probably trying to safe some money but you really should get an electrician to do this work.
Thanks for considered comment! It’s less about saving cash, it is a simple job but just don’t like the idea of channelling into walls.
 
Hi - just so you know - new regulations from January mean that changing the wiring on a circuit with lights will require an RCD be fitted, if it’s not already. And depending on details, a building works notification (Part P) might also be required as you are doing electrical work in a bathroom. An Electrician can help you with both of these aspects, as well as testing the completed works are safe, just saying :) .
It’s a WC
 
Surely anyone looking to service the fan will know it only operates when the light is switched on...

I’m thinking of changing an extractor fan (in a WC) to one with a run on/timer.

Hi mate. The fan will require a 'permanent live' as well as a 'switch live'. Both will need isolation, as well as the 'neutral'.
Have a look at the manual for the fan you are thinking of getting. This should tell you how to wired it.
What fan are you thinking of getting?
 
Hi mate. The fan will require a 'permanent live' as well as a 'switch live'. Both will need isolation, as well as the 'neutral'.
Have a look at the manual for the fan you are thinking of getting. This should tell you how to wired it.
What fan are you thinking of getting?
An Envirovent SilentT 100.

Now thinking I could run wires from lightbulb (which run direct to CU (in WC) via switch) and a permanent live from lightning circuit in attic to an isolator switch located in ceiling, adjacent to fan.
 
As @Tony Reidy asked above, "Why do you need to channel into the wall if all the wiring is in the flat roof "??
 
why not just leave the light on for 20 minutes? otherwise it's not essential as in a bathroom extracting steam, only fart gas. leave for the benefit of next user. :confused: :confused: :confused:
 
Single wire runs to switch in WC then up wall into flat roof void, then out at light socket. Linked from there to existing (non-timer) fan.

So there is a switch live wire going to the switch from the light?
There should be a 'permanent live', 'switch live' & 'neutral' at the light then. Can you not tap of these?
Does your CU have an RCD?
 
This seems to be following a familiar pattern.
DIYer asks for advice
Forum says no don't do that it would be wrong and possibly dangerous
DIYer says no it won't

From here it usually goes one of two ways. DIYer sees sense and employs the services of an electrician to protect their own safety and that of their family and property.
Or the forum end up being tarred as elitist scum whose trade is a doddle and we are only withholding information as we are rip off merchants.

I'm on the edge of my seat.
 
This seems to be following a familiar pattern.
DIYer asks for advice
Forum says no don't do that it would be wrong and possibly dangerous
DIYer says no it won't

From here it usually goes one of two ways. DIYer sees sense and employs the services of an electrician to protect their own safety and that of their family and property.
Or the forum end up being tarred as elitist scum whose trade is a doddle and we are only withholding information as we are rip off merchants.

I'm on the edge of my seat.
well, it's only 2 wires 3 wires, 4 wires. oh bugger, it's on fire.
 
So there is a switch live wire going to the switch from the light?
There should be a 'permanent live', 'switch live' & 'neutral' at the light then. Can you not tap of these?
Does your CU have an RCD?
Yes, CU is split rcd, with single 2.5mm T&E cable running (embedded) to wall switch (1m away) then (embedded) to roof void. If this was a 3 core wire instead of T&E I wouldn’t be posting on here ie I wouldn’t have a problem!

So I have Switch L and N. I’ll connect these to a fan isolator switch fixed into ceiling. Then run permanent live from lighting junction box in attic to same switch. That way, single switch will isolate for servicing, complying with regs.
 
This seems to be following a familiar pattern.
DIYer asks for advice
Forum says no don't do that it would be wrong and possibly dangerous
DIYer says no it won't

From here it usually goes one of two ways. DIYer sees sense and employs the services of an electrician to protect their own safety and that of their family and property.
Or the forum end up being tarred as elitist scum whose trade is a doddle and we are only withholding information as we are rip off merchants.

I'm on the edge of my seat.
Naval gaze all you want. Some of us have got work to do.
 
Yes, CU is split rcd, with single 2.5mm T&E cable running (embedded) to wall switch (1m away) then (embedded) to roof void. If this was a 3 core wire instead of T&E I wouldn’t be posting on here ie I wouldn’t have a problem!

So I have Switch L and N. I’ll connect these to a fan isolator switch fixed into ceiling. Then run permanent live from lighting junction box in attic to same switch. That way, single switch will isolate for servicing, complying with regs.
Forgot to say, cable connected to 6amp circuit breaker in CU.
 
Yes, CU is split rcd, with single 2.5mm T&E cable running (embedded) to wall switch (1m away) then (embedded) to roof void. If this was a 3 core wire instead of T&E I wouldn’t be posting on here ie I wouldn’t have a problem!

Oh. I get it now mate.

So I have Switch L and N. I’ll connect these to a fan isolator switch fixed into ceiling. Then run permanent live from lighting junction box in attic to same switch. That way, single switch will isolate for servicing, complying with regs.

But then you will have a fan circuit fed from two different breakers.
 
Oh. I get it now mate.



But then you will have a fan circuit fed from two different breakers.
Hallelujah! The lighting junction box in atTic is on a circuit that’s connected to same breaker in CU! So I won’t be linking different circuits!

If this now complies with all regs, then saves me a hell of a lot of hassle and mess of ripping into walls.
 
Hallelujah! The lighting junction box in atTic is on a circuit that’s connected to same breaker in CU! So I won’t be linking different circuits!

If this now complies with all regs, then saves me a hell of a lot of hassle and mess of ripping into walls.

We got there in the end mate. That's why we have to ask questions, to get the full picture.
 
We all wondered why you needed a fan with a run on timer just for a WC.
I now see why, the amount of .... you come out with, it’s gonna be knackered out in no time!
 

Reply to Extractor fan to timer type in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
436
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
408
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
990

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock