Discuss Three phase (No neutral ) EFLI testing on an RCBO in the UK Electrical Forum area at ElectriciansForums.net
Connect N snd earth lead to earth?No. Just connect the N lead to earth.
I have a three wire ‘no trip’ option. I need a neutral for this to work.Do you have a piggy back lead? If so, using it, yes you would have to connect both N and E to E.
Are you sure? So I have found with my Kewtech and piggy back lead I connect the N into the earth lead and hey presto I get Zs!I need a neutral for this to work
I have a three wire ‘no trip’ option. I need a neutral for this to work. I do have three leeds.
Are you sure? So I have found with my Kewtech and piggy back lead I connect the N into the earth lead and hey presto I get Zs!
Just spoke to Mega. The 1500 series does not support TP efli when an rc device is in curcuit. Only way is to temp swap out rccbo / bypass for duration of testing. He said i can try the running neutral but he felt this could impact the zs more than swapping out the protective device. The 1700 serries will support lo current testing for TP though.