Discuss Three phase (No neutral ) EFLI testing on an RCBO in the UK Electrical Forum area at ElectriciansForums.net
John-
Hi
I have a MFT1553 Mega tester. Is there a feature on the tester to test 3phase RCBOs when there’s no neutral present? Pretty sure mot. Was wondering if i could temporarily connect a neutral on a Wander lead and use the three wire test method?
John
Are you sure? So I have found with my Kewtech and piggy back lead I connect the N into the earth lead and hey presto I get Zs!
No, cant see how that would work, you still imbalance coils by dumping current down the earth. I tried any way on a single phase rcbo and it tripped. Will call mega but i think the only way is with a neutral connected to the rcbo by a lead back at the board. Thanks.
Just spoke to Mega. The 1500 series does not support TP efli when an rc device is in curcuit. Only way is to temp swap out rccbo / bypass for duration of testing. He said i can try the running neutral but he felt this could impact the zs more than swapping out the protective device. The 1700 serries will support lo current testing for TP though.
Reply to Three phase (No neutral ) EFLI testing on an RCBO in the UK Electrical Forum area at ElectriciansForums.net
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Hi , Currently doing a design project in college and I need to pick a circuit breaker ( In device rating and type) for a food holding equipment...
Hi Hope anyone can help Can someone give me advice on how to connect up a 3 phase to 13amp adaptor lead for carrying out PAT testing on 3...