Nov 17, 2021
South east
Hi all,
I’m getting confused as to what the DNO are going to be installing as there main supply and as you all may be aware they tend to be a little shy at replying back.
We have been told ukpn will be supplying us a maximum of 270kva to a block of 24 apartments.
I am assuming this will be 270 kva three phase, being 200 amps per phase (I can’t imagine it being 400 amps per phase)?
Could anyone confirm this in their past experiences?
I’m querying this as I need to know sizes for tails and isolators before they come to connect the main head.
Any help/advice be appreciated.
270kVA = 1174A single phase 230V = 392A 3-pase 400/230V. Basically 400A
I fear you are bit out of your depth here.
Give that a go... think 400A is what they are proposing, hopefully the head has got smaller as its a bit of a beast, lol
Reactions: pc1966
Thanks for reply. Would you happen to know roughly dimensions of the head. I’m hoping 600mm x 850mm (width x height) will be enough space.
UKPN will have supplied you with this information, if not then you can ask for it, along with their requirements prior to connecting.
It's not just the size of the cutout itself but also the working space around it that is required.
Also note that you have been given the maximum possible KVA of the supply, what you actually get may be less than that and will possibly be what was asked for on the application.
As others have said - without sounding unkind, are you confident in your abilities with this project?
If you register for access to the UKPN document library online you can view a lot of their design standards and drawings for standard new supplies.
For this question you may want to have a look at
EDS 08-1103 supllies to multiple occupancy buildings
EDS 08-2100 LV customer supplies (covers supplies from standard single phase up to 1500KVA)
EDS 08-2110-08, EDS 08-2110-10, EDS 08-2110-11, EDS 08-2110-19 are drawing of various different cutout arrangements that may apply to this particular supply.
I’m just asking for a bit of advice mate. As I have said……DNO not handing information over. Exactly why I’m on this site asking.
That’s great advise. Thanks a lot.
Bear in mind that tails for 400A are difficult to manage, even as singles, 240mm rings a bell but would have to check with the dno.
make sure there is plenty of space for the cable bends as they will be quite large, 300mm rad would not be unusual.
As mentioned, you really have to beat up DNO to provide their spec, you cannot be expected to guess what they are going to rock up with. The question in my mind is how is this all going to be distributed to 24 supplies, busbar chamber ?? - Where is the demarcation point for you in this scenario. I dont do flats just comm and industrial but somehow the 400A incomer has to turn into many smaller supplies and this takes up alot of space, probably a whole room with meters and the like. Hopefully someone on here can fill in how the single supply gets cut up for flats.
DNO standard for 260-300kVA will be 300mm^2
240mm^2 would cover 230-260kVA
  • Informative
Reactions: pc1966 and James
Is that for the supply cable Or the meter tails?
Hi all,
In my experience there is never any difficulty in obtaining the information from DNOs for this sort of thing, as has be already stated each DNO makes their generic information freely available.
I attach ENWL's versions of a couple of documents that would be appropriate in an installation of this nature as examples. Noting that all DNO's have their own version, which are usually virtually identical across all DNOs.
The only caveat is that DNOs will follow the contract path rigidly!
The connection agreement will be between the DNO and the customer - information will be freely available across this route, and if the customer tells the DNO, "Heyyall will be acting as our technical representative in this matter " then exact information would be directed through you. This would include all specific drawings and the like for this particular installation.
They will not divulge this information to a random third party, even if you are intimately involved with the project, from the DNO's perspective, you are a random third party.
This is great stuff thanks. The problem I have is that the developer has used a consultant from another company to deal with the DNO and therefore I am left out of the picture. Asking the Developers for info is like getting blood from a stone. But with this I’ll see if I can obtain direct contact with them passing my details on.
I've just had a 200kva supply put on to a new job, 315A fuses, they asked for 150mm tails, in trunking, chart they gave me is attached. Standard 70°c 6181y aswell.
That's really my point about third party.
From the DNO's perspective, and contract obligations not only are they not willing to give you this information; they will be contractually obliged to not divulge it.
They have most likely already provided it to the relevant party.
If this needs to be disseminated though to others, it is the responsibility of the developer.
Reactions: nicebutdim
I dont do flats just comm and industrial but somehow the 400A incomer has to turn into many smaller supplies and this takes up a lot of space, probably a whole room with meters and the like. Hopefully someone on here can fill in how the single supply gets cut up for flats.
From what I have seen it is usually a Ryefield board after the main isolator and any CT-based meter for the whole supply, but as you say it depends on where the meters are (if they are all per-flat so just some SWA or concentric to each flat with a red link in the cut-out, or if the switch-room has all meters in one place, etc.)
Hopefully there is a plan!
It looks like they have split it up differently to most DNO.
That supply was for a multi-occupancy building wasn't it?
Mine was just a new supply for a gym, just think he needs to bleed whatever stone is required to get that info just incase 😆
Reactions: pc1966
From what I have seen it is usually a Ryfield board after the main isolator and any CT-based meter for the whole supply, but as you say it depends on where the meters are (if they are all per-flat so just some SWA or concentric to each flat with a red link in the cut-out, or if the switch-room has all meters in one place, etc.)
There are a few arrangements, it could be group metering followed by distribution by a BNO, they can decide to distribute meters in each flat, or place them at the group metering point, or so on.
The Es287 document I attached previously describes the general options.
I would sincerely hope there is a plan, but this would be the preserve of the developer.
Reactions: pc1966
Ah, that may be different, but most keep to the same connection standard irrespective of single consumer, or multi-occupancy
South east
Please help DNOs KVA……??
Heyyall,
Julie.,