I'm sure you could borrow someones torque screwdriver and self calibrate your wrist against it :)
I don't carry a torque screwdriver on site either but I have a range of very accurate versions in our workshop that are about 15 years old and too expensive to carry around. I'm thinking about getting one of these new snazzy looking red and yellow plastic ones although I wouldn't use it very often with the type of work I do. I'm just interested how they're used in the UK and what the recognised usage practices are now they've been popular for a while.
I found a great torque screwdriver and bought it from a company that sells firearms and it wasn’t expensive at all.
Reactions: nicebutdim
I've invented a torque wrist calibrator, a small box with 10 screws on it each one lights up at the labelled torque. We can then verify our own hand power settings every morning.
I theory you could buy one of those cheap torque check boxes and actually practice hitting certain torques with your wrist.
You can buy a normal torque screwdriver for as little a £10 on Ebay , the only issue is they are not Vde rated for the Uk
Long time no see and I hope you're all doing well.
I see that torque screwdrivers have become the height of fashion in the UK over the last couple of years. I wondered what general practice has been adopted regarding their use.
Are electricians expected to;
Have a torque screwdriver on site at all times?
Check torque of all terminations in CU's / DB's they open or just any new terminations they make?
Check the torque of all terminations in any accessories they open?
Also;
Is acceptable to do torque testing live in a CU (assuming a VDE screwdriver)? Is a risk assessment required for live torque testing?
If torque testing is performed in a DB/CU do you just check screws for tightness or do you loosen off all terminations first then re-torque to the correct figure to eliminate overtightened connections as well as loose ones?
Scam members are expected to use a torque screwdriver for every termination to comply with the terms of their membership. What is done is another thing.
On an EICR, it might be expected to check terminations, but the requirements of an EICR are also minimum disturbance.
Any new terminations are expected to be completed with a torque driver; as I have said, this is a requirement of scam membership and is inferred in BS 7671.
It isn't a requirement to re-check every termination you come across.
It is not acceptable to torque terminations live unless this can be justified under the live working assessment in the law.
It is not reasonable to expect that it is necessary to do such a thing with the circuits energised.
To ensure that termination is at the correct torque, it is necessary to slacken it and then re-tighten it.
Hence, you are disturbing the connection, which is not good when doing an EICR.
Things could go wrong, or a latent defect could be introduced.
Such devices would need calibration in accordance with the screwdriver OEM instructions and/or any quality standards your company is working to.
Also, the scam membership requirements may have a calibration period.
The calibration period for a torque screwdriver would typically be annual.
Mind, if it fails, then you should strictly speaking revisit every connection made since the last calibration, like that is going to happen!
So, watch this space for the monthly check devices and scam requirements to check your drivers against the known source every month!
  • Informative
Reactions: Marvo
If it's not acceptable to torque live terminations why would you even bother to get a VDE rated torque screwdriver, you could just use a normal mechanics version which I'm sure would be considerably cheaper.
I've bought one now to see what all the hate is about. There's none available over the counter here at any of our electrical wholesalers so I had to get it on Amazon and the shipping cost as much as the damn tool. There's also no calibration facitily available here so I won't be able to use it in real life for very long. The one I got is a Draper and it comes as a kit with various handles and interchangable blades which are obviously proprietary fitting and you can't use Wiha or Wera blades or standard 1/4 in bits in it.
The H&S "bods" in the UK can't understand that people can work on isolated equipment without using insulated tools.
However, in their defence, the UK public distribution network is in such a poor state of repair that the PME/TN-C-S system using CNE/PEN conductors is breaking down and there are many more PEN failures than are reported.
A PEN failure can result in a rise in potential of N & E conductors, which could be unexpected and hazardous, to persons.
So then an insulated tool helps.
I once met a contractor that was thrown off site for not using insulated tools.
It was crazy really, yes, he was working in the main incoming DB, but, there was no supply to the building at the time!
Most Insulated hand tools really don't cost that much more than non-insulated hand tools.
A basic 6 piece Set of screwdrivers possibly costs a fiver more to buy them Vde rated.
I know we aren't supposed to work Live , but we all poke about in the odd board which is Live so is wise to use Vde rated screwdrivers
Which 'scam' are you referring to as I had my NICEIC annual assessment 2 weeks ago and he had no interest in asking about torque screwdrivers at all? We tested at a couple of CU's - continuity and insulation resistance. Removed cables were re-terminated in front of the assessor with no torque driver?
When I was with the NIC my area engineer was happy that I had one, and that was the end of the conversation, but, it was a tick on his form.
Mind it was a few years ago, maybe the policy has changed, or perhaps my engineer was a bit more by the book.
I don't know.
Just had a reminder email from CEF about the coming calibration day in Dundee. Looked at the list and seems they don't offer torque driver cal as one of the services.
  • Informative
Reactions: nicebutdim and DPG
I'm starting to think that under the trade descriptions act they should stop calling them calibration days.
It's very rare to find anyone who is willing to actually adjust a device. My experience has been that they check against the manufacturers tolerances and it either passes or doesn't. If it doesn't they suggest sending it off for specialist repair.
I tried 3 different tester-days with that Megger 1552, on the 2nd two I told them upon arrive that "it isn't within spec, can you adjust it" and was told "No.". I'm looking forward to finding out whether my own efforts scrape through the system soon!
Do they do 18v impact driver cal's?
Well I've had my new torque screwdriver for a couple of weeks, I wanted to use it as much as possible to see why it's such an emotive issue. Unfortunately I work on control centres, everything from populating and wiring new panels in our workshop to sitework on panels of all ages... some of which are very old.
The first thing I noticed was very few components over a year or two old had a torque spec readily available for their terminations. Some maunfacturers were better than others, most of the Allen Bradley items had a spec if you were willing to comb through the individual spec sheets but much of the Indian, Chinese, Taiwanese or even USA manufactured items had no termination torque spec available whatsoever.
Second thing I noticed is how much work it is to torque check even a small control panel. Lack of spec aside, just the process of loosening all terminations and resetting them with a torque driver is helluva time consuming with the constant readjustment and changing of screwdriver tips. I did one very small panel, probably 5 or 6 years old that consisted of 9 or maybe 10 contactors and relays, a timer, a current relay and a few circuit breakers, a dozen pilot lights and maybe 25 DIN rail terminals and it took me over an hour. It was the first and last panel I did.
I could see their advantage in use for a domestic sparky working on new installs or CU changes or in a manufacturing environment. For existing installations I think with losening and retorquing they're not practical and just to retorque without loosening there's better, safer and more convenient alternatives to find poor connections such as careful visual inspection and thermal cameras.
Torque Talk
Marvo,
Marvo,