Hi everyone,
I'm nearly on my AM2 test and really enjoy the industrial side of things so I thought I'd learn by asking.

I recently came across this note about IR testing PRIOR to connection? Can someone just explain how you would test if there was steel conduit and the earthing arrangement being on the other end of a building!?

"It is essential that, when performing an insulation resistance test between live and protective conductors, the protective conductors are connected to the earthing arrangement – that is, to the general mass of the Earth (Regulation 612.3.1 refers).

The connection to Earth is typically achieved by the protective conductor being connected to the main earthing terminal (MET) of the installation, to which the earthing and main protective bonding conductors are also connected, with the MET connected to the earthing arrangement (the distributor’s earthing facility (TN system) or the installation earth electrode (TT system), as applicable)."

Thanks everyone
 
I recently came across this note about IR testing PRIOR to connection? Can someone just explain how you would test if there was steel conduit and the earthing arrangement being on the other end of a building!?
I think there are two things being muddled:
1 - testing when using conductive containment, or MICC cable
2 - final IR testing prior to energising.

For the final testing, the containment would need be fully installed and earthed before you tested.
Then you would test the conductors in turn against the CPC bar or MET, whichever is nearer.

For the intermediate testing, it's a matter of testing all conductors against the containment (or MICC copper outer)

I can't remember what you have to do to pass the exam, but it just seems common sense to me to make sure that any containment that is conductive isn't in contact with any of the conductors.
 
  • Like
Reactions: Jim_e_Jib

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Newcastle
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
IR testing steel conduit on 1st fix?
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
sheppy619,
Last reply from
timhoward,
Replies
1
Views
1,241

Advert