Hi lads 5 year safety inspection the spark put the tails back and later line 2 of the 3 phase blew blowing the box off the wall and taking out the main fuse on the same line into the building can you all just say quickly what you think the spark may have done wrong ?
Cheers
IMG-20230317-WA0026.jpg
 
Last edited by a moderator:
Why did the spark have the tails out for an inspection?
No idea but it's a local council job so I assume because they can bill them for more dough
 
No idea but it's a local council job so I assume because they can bill them for more dough
Are you sure he actually did remove them? He should have spotted a loose connection when checking all the terminals though, thats if it was that and not faulty contacts in the switch.
 
Are you sure he actually did remove them? He should have spotted a loose connection when checking all the terminals though, thats if it was that and not faulty contacts in the switch.
Yes 100% he took them out and put them back in again
 
I would say a dead short has occurred there.
 
There is molten metal albeit it doesn't look like copper, the remains of something else?
 
  • Like
Reactions: jimthegent
Looks like the Red clamp has squashed the cable and split the insulation.
That's allowed the copper core to touch the earthed metal backplate and or the screw holding the clamp.

If it was the cable lose in the terminal or wrong side of termianl clamp it would have fizzled and overheated for a while before ultimately failing.

As Westwood, it looks like a dead short, especially with the ball of copper
 
There is molten metal albeit it doesn't look like copper, the remains of something else?
Yes the cover of the board was blown off and there's a lot of black soot all over the switches so clearly a lot of heat was generated
 
Looks like the Red clamp has squashed the cable and split the insulation.
That's allowed the copper core to touch the earthed metal backplate and or the screw holding the clamp.

If it was the cable lose in the terminal or wrong side of termianl clamp it would have fizzled and overheated for a while before ultimately failing.

As Westwood, it looks like a dead short, especially with the ball of copper
Yep now bear in mind all other tails and switches are pristine is there any votes for system overload the main fuse that blew into the building is also on phase 2
 
It is a dead short. Can you show a more direct pic below the red clamp.
 
Needs to be powered down and clamp removed, i can see it is already pinching the RHS cable sheath.

Once clamp removed photograph the back side of it, remove the LHS cable and photographc the back plain of board, should tell you everything you need to know, Merry Xmas
 
It is a dead short. Can you show a more direct pic below the red clamp.
Hi no they can back and replaced the switch and tail and removed the offending bits
 
Ah so its all sorted....
Seems the wire being nipped seems to be winning the vote can any of you guys see a situation were a nicely balanced 3 phase which was always well well under max amps would see just one phase go up like this
 
Ah so its all sorted....
Yeah but the upshot was that we were running on 2 phases for a a good few hours the fans failed the temp in the building rocketed and a load of other problems as a result
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Liverpool
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Manufacturer / Distributor / Supplier / Inventor - etc
Business Name
Mandalblit Services

Thread Information

Title
3 phase problem after spark did 5 year safety inspection
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
81

Advert

Thread statistics

Created
jimthegent,
Last reply from
jimthegent,
Replies
81
Views
8,299

Advert