How do you know your system is perfectly balanced? Why is that board fed in tails? Generally heavily loaded single phase boards would indicate the system is unbalanced in my experience. I can’t really see why the spark had the tails out for testing either, just doesn’t really make sense.

Edit- no answer to my previous question either, did the cover actually blow off? How did that happen with threaded screws on the cover, did they break? Do you have a picture?
There's a pic of inside the box there's black all up the rhs and inside it's black and scorched
 
How do you know your system is perfectly balanced? Why is that board fed in tails? Generally heavily loaded single phase boards would indicate the system is unbalanced in my experience. I can’t really see why the spark had the tails out for testing either, just doesn’t really make sense.

Edit- no answer to my previous question either, did the cover actually blow off? How did that happen with threaded screws on the cover, did they break? Do you have a picture?

Screenshot_20231224_222841_Gallery.jpg
 
Last edited by a moderator:
How do you know your system is perfectly balanced? Why is that board fed in tails? Generally heavily loaded single phase boards would indicate the system is unbalanced in my experience. I can’t really see why the spark had the tails out for testing either, just doesn’t really make sense.

Edit- no answer to my previous question either, did the cover actually blow off? How did that happen with threaded screws on the cover, did they break? Do you have a picture?
There's the best I can get of the burnt tail after it has been taken our
Screenshot_20231224_223850_Gallery.jpg
 
Last edited by a moderator:
But thats all hanging off that single phase board, so i dont get why you keep talking about phase balancing? How many amps are each of those servers drawing? If the full or near to the 16A that is mighty loaded, With that board connected straight off the henleys i wonder what the upfront main fuses are. Are they greater than 100A?
 
But thats all hanging off that single phase board, so i dont get why you keep talking about phase balancing? How many amps are each of those servers drawing? If the full or near to the 16A that is mighty loaded, With that board connected straight off the henleys i wonder what the upfront main fuses are. Are they greater than 100A?
Hi 5 amps a unit and yes the fuses are 100amp per phase there's a small drawn through the main board to run the fans but it's tiny
 
I just dip in and out of here when i get a sec, i really have no further ideas, thats not a massive load if all is well, but hefty if there was a poor main switch or loose wire
True there is a higher draw at start up as we need to get the building down to optimum temp and the fans on the machines work harder until we reach equilibrium but a loose wire is a disaster no matter what the load is isn't it
 
True there is a higher draw at start up as we need to get the building down to optimum temp and the fans on the machines work harder until we reach equilibrium but a loose wire is a disaster no matter what the load is isn't it


I still maintain its nothing to do with a balanced or unbalanced 3phase load.
I do not think it is an overload (you dont get flash/bangs like that and molten copper from an overload)
IMHO Its a L - E or N 'Dead Short'
 
I still maintain its nothing to do with a balanced or unbalanced 3phase load.
I do not think it is an overload (you dont get flash/bangs like that and molten copper from an overload)
IMHO Its a L - E or N 'Dead Short'
I think we all agree on that, but as it was running when the inspector left, something happened in between, the live side of the main switch has a significantly larger hole in the top compared to the neutral, so id say its sat there loose with 50A running through it getting mighty hot followed by a bit of arcy action first before it truly ---- itself
 
I still maintain its nothing to do with a balanced or unbalanced 3phase load.
I do not think it is an overload (you dont get flash/bangs like that and molten copper from an overload)
IMHO Its a L - E or N 'Dead Short'
Yeah and there's a lot of breakers on our system theres breakers in the pdu there are breakers on the main board surely it would just stop working with too much power drawn
 
This was what is left of a RCD that had been in service for years without being touched (even during an EICR a few months prior).
It was from an installation in a community hall which would have been drawing less than 20A at the time.
The 'Dead Short' caused the cutout fuse (100A) to 'blow'.
We concluded it was an internal failure of the RCD and not caused by recent activity (as there wasn't any) but why? Who knows, one of those things!
 

Attachments

  • RCD Dead Short IMG_0196.jpg
    48.3 KB · Views: 19
Looks like the Red clamp has squashed the cable and split the insulation.
That's allowed the copper core to touch the earthed metal backplate and or the screw holding the clamp.

If it was the cable lose in the terminal or wrong side of termianl clamp it would have fizzled and overheated for a while before ultimately failing.

As Westwood, it looks like a dead short, especially with the ball of copper
Good spot! It looks exactly that.
 
There have been several reports of Hager RCCBs detonating when the test button is pushed which then blows the cutout fuse, it also happened to me a few years back, really loud.
 

Reply to 3 phase problem after spark did 5 year safety inspection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
572
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello. I hope someone can help. I've just discovered that on a new build house built just over a year ago there is a problem with the wiring from...
Replies
11
Views
4K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock