M
Mat-sparks
Hi All,
I soon have my Assessment with Elecsa (1st one) a friend of mine needs some work doing so am going to take advantage of this and use it as my Major works...
I have a couple of questions though.. (as I am obviously nervous and worried about covering everything correctly)
My friend needs his new hot tub wiring up...
Hot tub requires (according to rating plate) a 230-240v 16a class c breaker. This is fine, I understand this.
My problem comes in the form of my friends CU being obsolete, so obtaining MCB's for it is a pain anyway let alone finding a Class C.
So The options are, Complete consumer unit change - Friend not so keen on this, which is understandable
Try my luck with a B type which I can get 2nd hand (assessor may not like this if he notices the rating plate says a C)
I could (and this is what I will probably do, subject to peoples opinions) fit a 32a type B to the spare way in the CU, then run 4mm T&E to a small garage style consumer unit which I will locate next to the original CU and in this fit a 16a type C. Then from this run 2.5mm armoured down to Garden and straight into rotary isolator that is supplied with Hot tub.
Or am open to suggestions.
Cheers
If it states on the instructions to use a type c then that's what you should install. No point in giving them ammunition to fail you on. The bgb says follow the manufacturers instruction.
ben
I take it you dont fancy tapping off the incoming tales, using henly block, for the new CU?
Yeah reading that all back it does sound a bit silly.
So as my firend doesn't want to replace the consumer unit, which I can't blame him on, as it's only around 8 yrs old and has RCD protection ETC, the only thing for it really is the seperate Consumer unit.
Just out of curiosity, what make is his CU?
can't see a 8 year old CU being obsolete. as spoon says, what is it? and a pic. would help here.
just had a look at an image of the siemens stratum 200:
the MCBs look like 3871s
go for a sub board & henleys here for this proposed install....
Am I being thick? The link is just to home page?
I've typed in the name of the CU and Siemens type C and nothing??
Pick SIEMENS MCB / RCBO from the MCB's list on the right hand side and see if any are suitable.
just get the correct MCB. from post #9.... ssimpless.
from the fuse company.siemens 5SY41, 16A type C.
Ok, I've stopped being stupid and found the correct ones on the Fuse company's website.
So 16a type in spare way on CU (already RCD protected by main incoming switch) out with armoured 2.5mm clipped to house wall, down to rotory isolator on hot tub. Job done!
Sounds good, in the meantime I phoned the fuse company, who gave me the number of another company selling recons' See if we can sell 35 years worth of collected MCB's :)
Sorry didn't see this, But will it go against me if he see's its a 20 instead of a 16?
no.
its the cable your protecting...hence my question at #19
it will require a minimum of 16A...with characteristic curves to type 3/C
like i says...as long as the cable CCC is good for it (after any correction factors have been aplied)...and the Zs is good...then off you go...
Also regarding earthing arrangements (I am yet to look at what install his is) and will have to hunt to find it as his CU is 2 3rds of the way up his hallway wall (my guess would be the small bin shed outside the front door) I am utter crap at remembering the different types and will check regs but are there any that will require my to supplement any extra bonding (earth ground spike) or will this all depend on Zs and Ze results regardless of what arrangement he has now?
find out what the earthing system is. measure your Ze. check bonding and allow for rectification if needed. don't forget, if it'
's TN-S and the bonding is 6mm, it's OK if it's intact and undamaged.
his unit looks slightly different to this but the MCB's are the same.
I really don't fancy doing it that way I I'm honest! I think it's a lot of work to fit a supply a 16a supply.
If a jobs worth doing and all that.
Its probably quicker easier cheaper to splits tails a put in a new small CU
If he installs a secondary board off the tails via henleys will the inspector moan about a lack of a seal on the meter or do they not look at that sort off thing?
Reply to Assessment / Install questions in the UK Electrical Forum area at ElectriciansForums.net
Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hi, I was looking at my dishwasher and it has this metal plate with these markings. I am confused about the meaning of "10/16A" - does that...
I have a small Consumer Unit fed from a 6 amp type B mcb to a 6 amp type B,it only feeds 1 light in a bin store . clearly we have no selectivity...